Hi Guys,

Does anyone know if there is a difference between the MEM Eaton MR30 and the H30 to convert MCB's to RCBO's?
Cheers in advance.
 
Hi Guys,

Does anyone know if there is a difference between the MEM Eaton MR30 and the H30 to convert MCB's to RCBO's?
Cheers in advance.
Looking at the products, the MR30 'pod' converts any standard Eaton SP or SP+N MCB into an RCBO, whereas the H30 device is an RCBO, which can be used to replace a standard Eaton MCB. For more accurate information you could contact Eaton Technical Support [email protected], a reply can take up to 48 hours.
 
Looking at the products, the MR30 'pod' converts any standard Eaton SP or SP+N MCB into an RCBO, whereas the H30 device is an RCBO, which can be used to replace a standard Eaton MCB. For more accurate information you could contact Eaton Technical Support [email protected], a reply can take up to 48 hours.
Thanks Shane,
I've seen both type listed on a site and they look identical! I'll email the support you've listed.
 
I don't know the exact reason but would it be anything to do with mechanical and electronic actions of the pod?. I say this because in a previous job we had these fitted and i remember with the one type our communications radios button only had to be pressed and the whole row of rcbo's operated on their own but when i changed them to the other type, they were fine.

Can't for the life of me remember which was which (old age lol) but might give someone more knowledgeable than me a bit of a starting point
 
Yes, we couldn't work out for ages what was causing the rcbo's to trip looking at all sorts of things as you can imagine, then one day i was in the vicinity of the MEM board and used my radio to speak to the boss and the rcbo's went off like a row of dominoes. Very strange.
 
MEM RCDs from the same era are known to be susceptible to nuisance tripping if situated too close to a 'smart' meter, so it's not unreasonable to think that RCBOs from the same stable may be prone as well.
 

Reply to MEM Eaton RCBO PODs in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Hope everyone has had a great Christmas and here’s hoping we all have a better new year coming our way ! Remember our riches aren’t measured by...
    • Friendly
    • Like
Replies
11
Views
551
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
760
  • Sticky
  • Article
Thanks so much for sharing this with us! I’ll definitely take a look, it seems like there are a lot of useful and interesting products. The idea...
    • Like
Replies
5
Views
2K

Similar threads

  • Question
Theres an FCU feeding external electric gates, an intruder alarm and I'm guessing more than 2 lighting feeds. It's been reported to the client and...
Replies
5
Views
449
  • Question
well then, must be a fault on the circuit, a faulty appliance if a power circuit or a faulty RCBO.
Replies
10
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top