Have a nightly problem - will be changing a consumer unit however have a problem customer has an older mem m6 32amp rcd/mcb on downstairs ring main only - this is tripping around 3-4am every morning told me had this off and on for a year. Not connected to anything on a timer eg heating / lights..
Unplugged / switched off everything and still happening , I have checked out circuit wiring and don’t have any faults also RCD test 1/2,x1,x5 and was ok - doesn’t happen during day so not been able to simulate
Anyone had this or wondering if some issue with older breaker / maybe voltage changes during night or something not thought off or just change our consumer unit and do more testing on wiring with all fully disconnected