or would it fail the latest requirements for an electrical report on a 4 bed town house?
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss Memera 2000 fuse box...is it legal now in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
I was told it was because the fuses divided into 2 halves and the main disconnecting switch was only on one side. I was given the estimate of ÂŁ350 plus ÂŁ350 for an electrical certificateas long as it's safe and complies with BS7671, no problem. i assume you mean because it's not metal cased.
Agree, someone is being naughty.Someone is telling porkies and only wants your money. Not ideal but not illegal.
Could you possibly post a picture to confirm?
Thank you that is very helpful. Any ideas on costs?it's not up to current regs., but would have been compliant with the regs. at the time it was installed. i would recommend upgrading, but only as a recommend. a bit like an advise on a MOT.it's a matter of choice whether you want to improve the safety of the installation, but not necessary.
there are 3 categories used on a condition report...
C1 is immediate danger. installation unsatisfactory.
C2 is potential danger... unsatisfactory.
C3 is improvement recommended, but satisfactory. i.e safe for continued use.
at worst, the CU might warrant a C3.
I was given the estimate of ÂŁ350 plus ÂŁ350 for an electrical certificate