Hi,
Just wondering what people interpretations of the regs are regarding metal CU's in a commercial setting. I've seen some people code them C3 on an EICR and others say that the Metal CU's are just for domestic settings. I've read the regs and I think they could be read either way. Anyone any definitive thoughts?
Thanks.
Andy
 
They really can't. The Regulation is very clear. Under no circumstances could a commercial property be considered to be "domestic (household) premises".

Sorry, I wasn't saying that. Reg 421.1.201 talk about domestic having to be metal cu's then 421.1.6 seems to talk more generally about materials used for enclosures. Maybe I'm reading it wrong.

When I've done commercial I've not coded it but I saw one from someone else who had put it as a C3 hence my question. Just want to make sure I had got it right and I'm not missing something.
 
Hi,
Just wondering what people interpretations of the regs are regarding metal CU's in a commercial setting. I've seen some people code them C3 on an EICR and others say that the Metal CU's are just for domestic settings. I've read the regs and I think they could be read either way. Anyone any definitive thoughts?
Thanks.
Andy
Completely disagree

It is absolutely clear, the regulation states "...Within Domestic (household) premises, consumer units and similar switchgear... ..enclosure manufactured from non-combustible material...." - How can this be read either way to apply to commercial?


I accept 421.1.6 says materials used shall be resistant to heat and fire, this is not the same as being non-combustible.
 
I just laugh and walk away, I find its best rather than argue with people...
 
the regulation about metal CUs in domestics bears no relevance to commercial installs.

there is no regulation specifying which type should be installed in commercial situations, so either metal or insulated boards comply, providing correct installation procedures are followed.
 
Hi,
Just wondering what people interpretations of the regs are regarding metal CU's in a commercial setting. I've seen some people code them C3 on an EICR and others say that the Metal CU's are just for domestic settings. I've read the regs and I think they could be read either way. Anyone any definitive thoughts?
Thanks.
Andy
Interesting question with every one working from home. If you work from home is that then a commercial environment. It maybe someone registered business address like a sparky
 
It's a dwelling.
It can't be a Commercial environment, the Dwelling won't have planning permission for commercial use.
It won't have a commercial mortgage.
It won't be insured as commercial.
 
Ermmmmm............ wtf??! Frankly anyone seriously needing to explore this question should consider retraining.
 
Ermmmmm............ wtf??! Frankly anyone seriously needing to explore this question should consider retraining.
Care homes, hospitals, prisons, hotels, flats over shops, shops under homes, etc.
Domestic, residential, homeowner, buy to let, social, private accommedation.
Public stairwells, communal areas, etc
I agree I nolonger understand the law but where is the advice/training the IET ?
 

Reply to Metal CU in a commercial setting in the Commercial Electrical Advice area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
388
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
969
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
This potential client seems to be making progress in terms of being interested in proper chargers and answering my query questions. I have also...
Replies
13
Views
2K
  • Question
Personally, I would take a Ze measurement myself rather than rely on someone else's maybe drive by scrap of paper.
2 3
Replies
31
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top