On one of my 'other jobs' which I mentioned the other day,
One building which is TT and fed by an SWA, although the earths are isolated and this building is protected by a rod, has single insulated cores feeding the incomer (100ma rcd).
However the whole installation is protected by a 300ma Time delay at source, so would the double insulation of the incoming cores still be necessary?

cheers
 
Erm, if I'm understanding you correctly, you've got a submain running to a building on two core and the earth to that board is by TT.

To turn your question around, if you wanted to change the incoming feed for singles then those cables would need additional protection - either by trunking/conduit/whatever or double insulation if being surface clipped.
 
Erm, if I'm understanding you correctly, you've got a submain running to a building on two core and the earth to that board is by TT.

To turn your question around, if you wanted to change the incoming feed for singles then those cables would need additional protection - either by trunking/conduit/whatever or double insulation if being surface clipped.
double insulation or insulation and sheething?..
 
double insulation or insulation and sheething?..

which is what I was meaning by 'whatever'. Basically, one layer between you and the copper is a bad idea.
 
Sorry original question a bit cr*p!

Basically, The origin of the installation is PME, The workshop and office are submains and connected PME, and I have upgraded the bonding.
This sub board feeds another building using 2 core SWA (16mm). This building is TT'ed as it could contain livestock, however the building has a metallic consumer unit being fed from the 2 core SWA.
As I understand a TT installation should have an insulated consumer unit or double insulation to the incoming cables,
BUT... as the whole installation is protected by a 300ma time delay at origin is this necessary?
 
Well, by the sounds of it you've got a correctly installed system, so why the question?
 
Just wasn't sure whether the Main RCD had to be at the origin of the TT installation or back at the origin of the whole installation, every time I have done a TT we have used an insulated board and have had a time delayed RCD mains switch,
Just thought this was a bit funny having a metalclad unit with the Time delayed being back at the origin.
However I can see nothing 'wrong' with it, just not something I have seen before.

The TT sub-board has a 100ma non-delayed RCD which is faulty, I may just replace this with a 100a dp main switch then as it is already RCD protected further back in the system.
 
Hi Somersetsparks , i can not make my mind up as to whether you need the shielding installed in the cu or not as you have the upfront 300ma !
I suppose it should be covered by it , but it just don't sit right with me for some reason ?
 
Just wasn't sure whether the Main RCD had to be at the origin of the TT installation or back at the origin of the whole installation, every time I have done a TT we have used an insulated board and have had a time delayed RCD mains switch,
Just thought this was a bit funny having a metalclad unit with the Time delayed being back at the origin.
However I can see nothing 'wrong' with it, just not something I have seen before.

The TT sub-board has a 100ma non-delayed RCD which is faulty, I may just replace this with a 100a dp main switch then as it is already RCD protected further back in the system.

No way !
If i have read the post right , the shed would not be protected correctly .
 
Hi Somersetsparks , i can not make my mind up as to whether you need the shielding installed in the cu or not as you have the upfront 300ma !
I suppose it should be covered by it , but it just don't sit right with me for some reason ?

Same with me, hence the question. Theres not really anything wrong but It just doesn't seem right!
I am in the rare situation of working for a farmer (a mate) who likes to have things done properly, although he still insists on running cables, digging trenches etc. Which is fine with me!

I may double insulate the incoming SWA cores for good measure, has anyone done this before and have a good method of achieving it?
 
As for the knacked 100ma one , I know this will get a bit of flack but I would replace it with a 30ma .
I know it will take the whole board out , but even if you replace it with a 100ma and use rcbo's you have lost any discrimination as the 100ma will not be a s type .
 

Reply to Metal Fuseboard on TT in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
303
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
819
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
896

Similar threads

  • Question
much more information required. Is the supply to the first building a DNO supply or a sub main cable from another building ? if it is a sub main...
Replies
5
Views
950
  • Question
I think there is a little truth in what the guy in the video says, but he makes more out of it than he should. A N-E fault on a circuit protected...
Replies
28
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top