Hello
I attended a customers property today to check on a fault with some latern courtyard lamps. There are 4 lamps and the centre 2 are not working. The customer had replaced the bulbs himself but there was no joy.

As a first port of call I swapped the 2 working bulbs from the outer fittings with the unworking bulbs to rule out bulb failure. Once swapped the bulbs are fine with the outer two fittings but still no light on the centre 2.

I used a lightmate on the centre fitting and voltage is present at 230v. The customer was not present in the property at the time so I could only access the yard however there is no sign of any ballast anywhere near the lamp. The lanterns are attached to a high wall (perhaps 20ft) with pillars which the lights sit on. The flex from the fitting simply disappers down inside the pillar. I have done work at his property before and there is a room containing all the consumer units, AV gear and switchgear for the property but I cannot for the life in me remember seeing any ballasts for sodium/halide lamps in there, just armoured cable for the courtyard lighting exiting the room underground.

I didn't have my multimeter with me so the only test I could run was that voltage was present and even to check the fitting was tight used a normal BC energy saver which lit in all fittings.

What should my next course of action be? I'm not going to lie I don't have a huge wealth of experience with arc lighting. The customer had reported that the RCBO supplying the courtyard lighting (C6 RCBO) had tripped a couple of times prior to him changing these 2 bulbs after which there has been no more tripping.

Does this sound like the ballast itself is at fault? I think I already know the answer to this but would you think the original fitter have been stupid enough to encase the ballast within the pillar or even under the driveway for some reason?
The bulbs in question are these http://www.venturelightingeurope.com/products/whitelux-plus-lamps/13742.html which appear to be a direct swap for HPS lamps using the original ballast
 
Hello
I attended a customers property today to check on a fault with some latern courtyard lamps. There are 4 lamps and the centre 2 are not working. The customer had replaced the bulbs himself but there was no joy.

As a first port of call I swapped the 2 working bulbs from the outer fittings with the unworking bulbs to rule out bulb failure. Once swapped the bulbs are fine with the outer two fittings but still no light on the centre 2.

I used a lightmate on the centre fitting and voltage is present at 230v. The customer was not present in the property at the time so I could only access the yard however there is no sign of any ballast anywhere near the lamp. The lanterns are attached to a high wall (perhaps 20ft) with pillars which the lights sit on. The flex from the fitting simply disappers down inside the pillar. I have done work at his property before and there is a room containing all the consumer units, AV gear and switchgear for the property but I cannot for the life in me remember seeing any ballasts for sodium/halide lamps in there, just armoured cable for the courtyard lighting exiting the room underground.

I didn't have my multimeter with me so the only test I could run was that voltage was present and even to check the fitting was tight used a normal BC energy saver which lit in all fittings.

What should my next course of action be? I'm not going to lie I don't have a huge wealth of experience with arc lighting. The customer had reported that the RCBO supplying the courtyard lighting (C6 RCBO) had tripped a couple of times prior to him changing these 2 bulbs after which there has been no more tripping.

Does this sound like the ballast itself is at fault? I think I already know the answer to this but would you think the original fitter have been stupid enough to encase the ballast within the pillar or even under the driveway for some reason?
The bulbs in question are these Whitelux Plus Lamps - 13742 which appear to be a direct swap for HPS lamps using the original ballast

Can't you open up the pillar to check? First course of action methinks. And yes, I am Shakespeare.
 
I'll try and get some pictures when I go back to the property but to be fair without actually 'breaking into anything' its going to be hard to see anything from the pictures. The light fittings are just lanterns over a bayonet cap fitment in the middle (all heavy duty external stuff). There is an adaptor to ES screw fitment with the bulbs in. The only 'electrical' connections in the lamp are 1mm flexible cable leaving the bulb fitting and going under the 'flag' at the top of the stone pillar.

The distance from the house is maybe 10M, even if the ballast was sited in the room with all switchgear would it work remotely like this? As stated before my experience with arc lighting is just fitting simple spotlights not using remote ballasts like this.

Would there be a test I could conduct at the fitting to confirm that indeed a ballast (or ignitor) was at fault before I have to start removing blocks or otherwise hunting for these?
 
There is no reflector, the lamp looks like this:

[ElectriciansForums.net] Metal Halide Lamp failure


The 'fitting' in the middle for the bulb is EXACTLY as shown in that picture and the only connection under the fitting is 1mm flexible cable that leads down into the pillar/wall to which it is fitted. There is nothing ballast or ignitor related within the lamp itself.
 
Has it a bc to es40 adapter fitted and a self ballasted lamp ? if so the lamps you are fitting wont work.

see PREMIUM QUALITY SELF BALLASTED 250W METAL HALIDE LAMP E40 5000K TUBULAR FITTING | eBay

the above is just an example there are loads more types available and connect directly to 220v mains (dont need a ballast)

The customer refitted these new bulbs and for some reason described them as 'wrong' although couldn't tell me why?

The adaptors are BC - E27

There are 4 lamps and this problem is only affecting the inner 2, they are all the same although perhaps the outer two are ballasted and the inner two are not?? Swapping bulbs from the inner to the outer makes no odds, it's still the two outer lamps which remain lit. Strangely enough an energy saving CFL BC bulb works in all 4 lamps
 
As an eBay Associate we earn from qualifying purchases.
The customer refitted these new bulbs and for some reason described them as 'wrong' although couldn't tell me why?

The adaptors are BC - E27

There are 4 lamps and this problem is only affecting the inner 2, they are all the same although perhaps the outer two are ballasted and the inner two are not?? Swapping bulbs from the inner to the outer makes no odds, it's still the two outer lamps which remain lit. Strangely enough an energy saving CFL BC bulb works in all 4 lamps

That's because it's a normal bloody lampholder.
 

Reply to Metal Halide Lamp failure in the UK Electrical Forum area at ElectriciansForums.net

Similar threads

I don't think I'd use it mate even the one line heading then one long paragraph screams ai. And untrustworthy. I don't think much has been edited...
    • Optimistic
Replies
3
Views
880

Recommended Sponsor News

Quickwire Now Sponsor ElectriciansForums.net

I am sure you will join me in welcoming our newest sponsors of ElectriciansForums.net - Quickwire! They have decided to join us after seeing you guys discussing their products here. Now we have an expert on board that you can chat to @Quickwire-Sam who will be happy to answer your queries!

[ElectriciansForums.net] Quickwire Now Sponsor ElectriciansForums.net


@Quickwire-Sam said "At Quickwire, we're all about speed, safety, and reliability. We're a family-run business, and every Quickwire connector is proudly made right here in the UK, ensuring noticeable quality. In short, Quickwire is the fastest connection method on the market. Whether you're an experienced electrician or a DIY enthusiast, Quickwire makes electrical connections ridiculously quick and easy. We're passionate about blending British craftsmanship with innovation. If you have any questions or if there's any way we can help, please just ask me!"

Exclusive Forum Offer! Free euro 2024 wall chart for first 10 responses!

Hi everyone,

We have 10 exclusive Uheat EURO 2024 Wallcharts to giveaway for Electricians Forum Members! The first 10 people to reply YES to this thread - I will message and get them sent out to you just in time for this years tournament! GO GO GO

PCBWay Now Sponsor ElectriciansForums.net!!

I hope you will all join me in welcoming our newest sponsor to the forum PCBWay! You can contact their friendly people by sending a message to @PCBWay who will be happy to answer your queries.

Welcome to the community and thanks for your sponsorship!

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

PCBWay provides services including PCB Prototype and batch Production, PCB Assembly (SMT), 3D Printing, CNC Machining, PCB Design, Electronics Modules Selling, etc. We are committed to meeting the needs of global makers from different industries in terms of quality, delivery, cost-effectiveness, and any other demanding requests in electronics.

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top