Metal lamppost in garden... TNC-S | Page 2 | on ElectriciansForums
Discuss Metal lamppost in garden... TNC-S in the UK Electrical Forum area at ElectriciansForums.net
United Kingdom
Evening all,
Need some opinions on this one please:
TNC-S house, complete new install, all going to plan, nearly finished second fix, customer then arrives with a huge metal lamppost (bought from Frinton-on-sea promenade...) and wants it hooked up in the back garden.
What is the general consensus on this - my concern is: in the event of loss is supply neutral, everything connected to MET, including that lamppost, will rise to a voltage, anyone touches it may get a shock?
Or, will the fact it's planted in the earth keep any possible voltage down?
Am I making something out of nothing here or would this be safer as a TT?
Any thoughts welcome.
Well you cud'a knocked me down with a feather when I saw this, normally it's only sheds that bring people out in a cold sweat when TNCS is mentioned. I think I've pointed out before that those who come over all unnecessary at the mention of a shed never seem to get that queasy feeling with other outdoor installs.
So good on'yer Weevilward, shows you are thinking about what you are doing rather than just following the herd and subscribing to myths.
I was in a conundrum some time ago, when a customer wanted me to connect up a previously installed metal lamp post at the bottom of their driveway. It wasn't a full lamppost, but one of the smaller ones mounted on brick wall. However, it was located adjacent to the public footpath. The property had a PME supply, and a swa cable had been previously installed. The CU didn't have a spare way for additional protection by RCD or compatible new RCBO's.
I read chapter 714, BS7671, outdoor lighting installations. This chapter seems only applicable to outdoor lighting in the public domain, street lighting etc. Whilst a light in someone's garden, is more under control and constant supervision than a street light would be, it does seem strange to have some many regs and guidance specifically for street lights and none per say for domestic lighting situations?
My conundrum was the additional protection. Advice from my scheme, in these circumstances, was to provide RCD protection.
This is what I was refering to in me post yesterday i did not have the byb with me at the time, just had a look now and as you say it refers more about street furniture but it does say it includes gardens under the scope 714.1 (i) so i would use this section of the regs for the ops installation 714.411.203 covers pme
I'm struggling here - if neutral was o/c any current flow would unbalance the device and cause it to trip (?)
No imbalance as the same amount of current will flow between live and neutral in the rcd but if in pme the earth would also rise to possible mains voltage if supply neutral is broken back to the source of supply (DNO cable)
There's no imbalance so rcd won't operate
Is the problem with o/c neutrals not more to do with overloading the 1.0 / 1.5mm2 cpc if all the neutral current (including from shower, cooker etc) is trying to get back to the supply neutral via said cpc, rather than anything to do with shock? And isn't that why we have to run 10mm2 main bonding wherever we take power from a PME supply (because this is the smallest that would be unlikely to be overloaded in these circumstances)?
If the neutral is broken at the supply side on pme then the current will be unable to return to the source via the neutral and as there is a link in the cut out that only exists in pme between neutral and earth then the current will flow through the earthing conductor and through all connected cpcs and bonding conductors.
Yes 10mm to deal with neutral currents.
Potentially putting very high currents through very small CPCs if these are connected to earth (e.g. by this lamp post) and the PME still has connections to earth on the supply side of the break.
So surely the OP should be putting 10mm2 bonding in place to this lamp. Or else somehow insulating it from earth.
Reply to Metal lamppost in garden... TNC-S in the UK Electrical Forum area at ElectriciansForums.net
Hope everyone has had a great Christmas and here’s hoping we all have a better new year coming our way ! Remember our riches aren’t measured by...