I was replacing some sockets today to metal face plates for customer in their extension. Lights have also metal face plates, and these are earthed. They bought some more metal switches to replace the ones in original house but I found out there is no earth in this part. I believe they can't have metal switches without earth and advised this, but they are not convinced. Does anyone know if there's a reg number I can show them as my reg book got pinched and waiting for new one. Thanks all.
 
loads of threads on this subject. jf they have plastic switches with no cpc, they must NOT be replaced with metal ones. end of.
 
411.3.1.1 a protective conductor must be run to every wiring point in the installation and every accessory, and all exposed conductive parts must be earthed.

However I am not sure how you are going to show them if you have no regs book.

The point is if the metal becomes live it does not kill you, it automatically disconnects instead.
 
Last edited:
Dillb sorry to swerve the thread but just to let you know I have nominated you to choose tomorrow's winning number on the prize draw.
 
If you want you can demonstrate the potential harm to the customer, one probe in their left hand, metal switch in their right. A croc on the switch and whack 500v through them.
They'll get the message :)
 
Thanks for the replies. Thought I was right, I'll just put them straight.

Come on Dillb, give us a clue, what number you thinking of for tomorrow, and what's the prize ?
 
I was replacing some sockets today to metal face plates for customer in their extension. Lights have also metal face plates, and these are earthed. They bought some more metal switches to replace the ones in original house but I found out there is no earth in this part. I believe they can't have metal switches without earth and advised this, but they are not convinced. Does anyone know if there's a reg number I can show them as my reg book got pinched and waiting for new one. Thanks all.
Put one of the switch screws through the live cable and let the customer decide for himself
 
just connect the switch L to the earth terminal, then tell them to switch the light on.
 
As well as explaining the regulations to them maybe you could also explain the reason why the metal switches come with an earth terminal. Also show them a plastic switch and explain why this one has no earth terminal.

:smile:
 

Reply to Metal switches, no earth. in the Electrical Course Trainees Only area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
265
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
756
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
743

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top