O
Octopus
He must mean max Ze 0.35. As for 25mm Tails, there must be thousands of PME systems out there on 16mm tails and 10mm Earth.
he's been looking at the picky in the OSG!
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss Meter tails and main earth in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
He must mean max Ze 0.35. As for 25mm Tails, there must be thousands of PME systems out there on 16mm tails and 10mm Earth.
Right, you've got a Zdb of 0.38.
That equates, (roughly, depending on actual voltage) as a PFC of 460A
What is the cut-out fuse size?
Is it a 63A as you stated, or is that an isolator?
So, assuming it is a 63A BS88-3, it will trip in one second - is this a homework question, as 460A is right there on page 296.
Do the adiabatic, and you get a 4mm earth conductor.
But then you need to cross-reference to 544.1.1 which states that a 10mm earth conductor is the minimum for a TN-C-S (PME) system.
So 10mm is required.
However, is the main earthing terminal in the CU, or at the isolator?
TNCS requires a minimum of 25mm tails and 16mm earth conductor.
Hi Alan,
thanks for the reply, the isolater is one of the old fashioned ones with the arm which only allows you to open the door when you have turned it off, and yes inside it has a bs88 63a fuse. The main earthing terminal is at the isolater. Why, what you thinking? It's a real install by the way, not a homework question. Thanks again.
Absolute nonsense
If the MET is at the isolator, and the earthing conductor, and the main protective bonding are up to current standards, connected at the MET, (10mm + according to tails etc), then (without doing the calcs), the 16mm T+E will be fine supplying the CU, as that will be a sub-main.
Work out if the CPC of the 16mm T+E is enough by testing the PEFC and PSCC, then doing the adiabatic.
From the info given, I would say yes, but check yourself.
Then you have the problem of the higher Zs at the DB.
6 metres of 16mm T+E cable will add around 0.05 ohms to the Zs, so there is either a bad connection somewhere, or the incoming supply has a high Ze, which is not uncommon, especially if the supply is at the end of its run in a road etc.
From the sub board you would be measuring Zdb as Ze is origin only, the Zdb would need to be low enough for max disconnection times of the 63amp fuse to be met , 5 seconds as its a distribution circuit.
Pretty sure the op mentioned the isolator has a BS88 63A inside.
Reply to Meter tails and main earth in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net