Hi guys,
Been to a one bedroom retirement bungalow today, supply is tncs into a cupboard just outside the front door, it goes into a 63a isolater then it goes from there into the roof void and into the consumer unit which is approx 6 meters from the isolater. The board is supplied via 16mm t+e with a 6mm (or perhaps 4mm) main earth. The ze was .50 which is obviously too high, I have now installed a 16mm main earth and the ze is now .38 which I am aware is still a fraction too high. My question to you all, is I am right in saying that the old earth was too small as I'm sure that it should be at least half the size of the meter tails.
They had another more experienced electrician do a pir a couple of weeks ago and he didn't mention it.

Im sure I'm correct in what I'm thinking, but you know what it's like, doubt starts to kick in and I would love to hear what you think.
 
Me thinks you be right! I always run a 10mm earth with 16mm t&e and then use the earth in the twin too! Hope this helps
 
As above, I'd imagine the ze at source to be highish..... Plus another 6meters, tipping it over.

id agree that the 4mm was easily too low, 10mm minimum IMO....
 
It's all academic anyway when you look at the tolerances of meters. Easy to loose a few thousanths of an Ohm :-)
 
TNCS minimum Ze is 0.35ohms. If it's outside this you need to inform the supply company to investigate.
TNCS requires a minimum of 25mm tails and 16mm earth conductor.
 
Surely the adiabatic equation will tell you if you have a sufficient sized Earthing conductor.
 
He must mean max Ze 0.35. As for 25mm Tails, there must be thousands of PME systems out there on 16mm tails and 10mm Earth.
 
Right, you've got a Zdb of 0.38.
That equates, (roughly, depending on actual voltage) as a PFC of 460A
What is the cut-out fuse size?
Is it a 63A as you stated, or is that an isolator?
So, assuming it is a 63A BS88-3, it will trip in one second - is this a homework question, as 460A is right there on page 296.
Do the adiabatic, and you get a 4mm earth conductor.
But then you need to cross-reference to 544.1.1 which states that a 10mm earth conductor is the minimum for a TN-C-S (PME) system.
So 10mm is required.
However, is the main earthing terminal in the CU, or at the isolator?
 
Right, you've got a Zdb of 0.38.
That equates, (roughly, depending on actual voltage) as a PFC of 460A
What is the cut-out fuse size?
Is it a 63A as you stated, or is that an isolator?
So, assuming it is a 63A BS88-3, it will trip in one second - is this a homework question, as 460A is right there on page 296.
Do the adiabatic, and you get a 4mm earth conductor.
But then you need to cross-reference to 544.1.1 which states that a 10mm earth conductor is the minimum for a TN-C-S (PME) system.
So 10mm is required.
However, is the main earthing terminal in the CU, or at the isolator?


Hi Alan,
thanks for the reply, the isolater is one of the old fashioned ones with the arm which only allows you to open the door when you have turned it off, and yes inside it has a bs88 63a fuse. The main earthing terminal is at the isolater. Why, what you thinking? It's a real install by the way, not a homework question. Thanks again.
 
Hi Alan,
thanks for the reply, the isolater is one of the old fashioned ones with the arm which only allows you to open the door when you have turned it off, and yes inside it has a bs88 63a fuse. The main earthing terminal is at the isolater. Why, what you thinking? It's a real install by the way, not a homework question. Thanks again.



Interlock Bill was his name
icon7.png
 
If the MET is at the isolator, and the earthing conductor, and the main protective bonding are up to current standards, connected at the MET, (10mm + according to tails etc), then (without doing the calcs), the 16mm T+E will be fine supplying the CU, as that will be a sub-main.
Work out if the CPC of the 16mm T+E is enough by testing the PEFC and PSCC, then doing the adiabatic.
From the info given, I would say yes, but check yourself.
Then you have the problem of the higher Zs at the DB.
6 metres of 16mm T+E cable will add around 0.05 ohms to the Zs, so there is either a bad connection somewhere, or the incoming supply has a high Ze, which is not uncommon, especially if the supply is at the end of its run in a road etc.
 
If the MET is at the isolator, and the earthing conductor, and the main protective bonding are up to current standards, connected at the MET, (10mm + according to tails etc), then (without doing the calcs), the 16mm T+E will be fine supplying the CU, as that will be a sub-main.
Work out if the CPC of the 16mm T+E is enough by testing the PEFC and PSCC, then doing the adiabatic.
From the info given, I would say yes, but check yourself.
Then you have the problem of the higher Zs at the DB.
6 metres of 16mm T+E cable will add around 0.05 ohms to the Zs, so there is either a bad connection somewhere, or the incoming supply has a high Ze, which is not uncommon, especially if the supply is at the end of its run in a road etc.

ive looked at a couple of these and they all seem to have highish ze, it is a rural location and I'm guessing the transformer is quite a long way away, my main concern was that I was right to say that the main earth needs upgrading. Thanks to all that have replied, it's nice to get other people's opinion, everyday is a learning day.
 
Am I right in saying aslong as your ze at the origin of the installation ( before the isolator) is less than 0.35 ohms.
The Ze at the sub board should not be greater than the max zs of the 63a fuse at the fused isolator.
 
From the sub board you would be measuring Zdb as Ze is origin only, the Zdb would need to be low enough for max disconnection times of the 63amp fuse to be met , 5 seconds as its a distribution circuit.
 
From the sub board you would be measuring Zdb as Ze is origin only, the Zdb would need to be low enough for max disconnection times of the 63amp fuse to be met , 5 seconds as its a distribution circuit.

I agree the Ze is the external earth loop reading so should be taken at the origin in this case the main isolator, the reading at the CU will be the Zs.
 
I suspect the "63a isolator" is not an overload or short circuit device, maybe a 63A RCCB?

in which case the ZDb does not need to match this value, it just, as has been stated by a n other, needs to be low enough for subsequent PDs to operate in time.
 
If its got an isolator between the db and the primary fuse wouldn't it be classed as a submain, therefore your zdb would not be classed as your ze because your ze has to be less than 0.35, whereas your zdb would have to be less than the max zs of the 63a fuse in the isolator, that's how I see it.
 
Ahh yes OP did comfirm later that there is a 63 Amp fuse in a container. Damn this Stella.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined

Thread Information

Title
Meter tails and main earth
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
30

Advert

Thread statistics

Created
Pondy,
Last reply from
SPARTYKUS,
Replies
30
Views
7,215

Advert

Back
Top