Meter tails and main earth
Right, you've got a Zdb of 0.38.
That equates, (roughly, depending on actual voltage) as a PFC of 460A
What is the cut-out fuse size?
Is it a 63A as you stated, or is that an isolator?
So, assuming it is a 63A BS88-3, it will trip in one second - is this a homework question, as 460A is right there on page 296.
Do the adiabatic, and you get a 4mm earth conductor.
But then you need to cross-reference to 544.1.1 which states that a 10mm earth conductor is the minimum for a TN-C-S (PME) system.
So 10mm is required.
However, is the main earthing terminal in the CU, or at the isolator?
Hi Alan,
thanks for the reply, the isolater is one of the old fashioned ones with the arm which only allows you to open the door when you have turned it off, and yes inside it has a bs88 63a fuse. The main earthing terminal is at the isolater. Why, what you thinking? It's a real install by the way, not a homework question. Thanks again.
Hi Alan,
Interlock Bill was his name
If the MET is at the isolator, and the earthing conductor, and the main protective bonding are up to current standards, connected at the MET, (10mm + according to tails etc), then (without doing the calcs), the 16mm T+E will be fine supplying the CU, as that will be a sub-main.
Work out if the CPC of the 16mm T+E is enough by testing the PEFC and PSCC, then doing the adiabatic.
From the info given, I would say yes, but check yourself.
Then you have the problem of the higher Zs at the DB.
6 metres of 16mm T+E cable will add around 0.05 ohms to the Zs, so there is either a bad connection somewhere, or the incoming supply has a high Ze, which is not uncommon, especially if the supply is at the end of its run in a road etc.
ive looked at a couple of these and they all seem to have highish ze, it is a rural location and I'm guessing the transformer is quite a long way away, my main concern was that I was right to say that the main earth needs upgrading. Thanks to all that have replied, it's nice to get other people's opinion, everyday is a learning day.
Am I right in saying aslong as your ze at the origin of the installation ( before the isolator) is less than 0.35 ohms.
The Ze at the sub board should not be greater than the max zs of the 63a fuse at the fused isolator.
From the sub board you would be measuring Zdb as Ze is origin only, the Zdb would need to be low enough for max disconnection times of the 63amp fuse to be met , 5 seconds as its a distribution circuit.
I agree the Ze is the external earth loop reading so should be taken at the origin in this case the main isolator, the reading at the CU will be the Zs.
I suspect the "63a isolator" is not an overload or short circuit device, maybe a 63A RCCB?
in which case the ZDb does not need to match this value, it just, as has been stated by a n other, needs to be low enough for subsequent PDs to operate in time.
If its got an isolator between the db and the primary fuse wouldn't it be classed as a submain, therefore your zdb would not be classed as your ze because your ze has to be less than 0.35, whereas your zdb would have to be less than the max zs of the 63a fuse in the isolator, that's how I see it.
Pondy,
SPARTYKUS,