Carlos ... you been a Trainee would be better asking these questions in the Trainee section, not everyone will note your a Trainee in the main forum before answering and can lead to off putting replies.
Their are no regulations stating the size of the tails, as has already been mentioned your tails are designed for the upfront fuse in this case and as we usually don't have access to the DNO fuses we must assume in domestic it may have a 100amp fitted.
Tails can utilise another regulation where the actually demand on them is restricted by the load they supply so say you had a 1way board for a shower then your tails could be say 10mm because the 40amp - 50amp rated fuse for said shower would ensure the demand on the tails could not exceed its CCC. This is limited to cables < or = to 3m.
So it is just the norm to fit 25mm tails on larger multi-way boards when the DNO fuse carrier is 100amp regardless of the rating of the fuse inside which we normally cannot access.
As for schoolboy errors ... don't worry about it we all did and some still do them, jeez I just found out it brown thats the Live one now that's 25yrs of plug tops I need to rewire.:sick: