meter tails in cavity wall | on ElectriciansForums

Discuss meter tails in cavity wall in the Australia area at ElectriciansForums.net

S

scott g

just been to qoute a fuse board change meter tails in 16mm 80amp main fuse in meter head cutout
question is changing fuse board and tails but i think im going to have to put a 30ma 100 amp rcd time delay on
tails is this the only way to get round this problem with tails in cavity?

Do ‘meter tails’ concealed in walls or partitions need to be protected in accordance with Regulations 522.6.6 and/or 522.6.8?

NDA4
Yes. Meter tails concealed in a wall or partition at a depth of less than 50 mm from a surface must be protected in accordance with Regulation 522.6.6. Also, irrespective of the depth from a surface, meter tails concealed in a wall or partition having internal metallic parts (except nails and screws, etc) are subject to the requirements of Regulation 522.6.8.

However, additional protection for meter tails by means of an RCD is not an acceptable option in respect of Regulation 522.6.7 (which in consequence rules out reliance on 522.6.6(v), routing in the ‘safe zones’ alone), or in respect of Regulation 522.6.8(v). Also, for TT systems, the only option remaining is to provide suitable mechanical protection (that is, to comply with Regulations 522.6.8(iv) and/or 522.6.6(iv) as appropriate).
 
Last edited by a moderator:
you haven't made your question very clear, r u saying that the meter tails are going through a wall cavity before they get to the meter from the supply fuse?

if that is the question, have you thought about either sticking the tails (if possible) in steel conduit or using SWA as they go through the wall?
 
Last edited:
If there are existing in the cavity already and they are to be changed
I pull the new ones through and use flexible ductingjng just in case of insulation problems

This is a popular dilemma for many sparks,some use safe zones and mechanical protection others use swa

Older farts like me, continue with poor cavity methods that the sparks with damp tracking concerns detest, and where thousands upon thousands of new builds have that same method
 
Last edited:
Hi all, I'm interested to know if you interpret this requirement the same if the tails pass directly through the wall, as opposed to running for any length along the cavity, if you see what I mean.
 
Hi all, I'm interested to know if you interpret this requirement the same if the tails pass directly through the wall, as opposed to running for any length along the cavity, if you see what I mean.

RCD requirement?

In that case no as the cables are not buried.

IE from outside to inside straight through.
 
Hi there,

I'm just about to change the consumer unit and tails at clients house. Upgrade to 25mm tails and Dual RCD board from 100A fuse located in meter cupboard on external wall. My question is, what would be considered to be suitable containment for meter tails? Tails come from back of meter cupboard through wall into garage, then up wall, approximately 1 metre then into consumer unit. I am being especially cautious with my selection of equipment on this job as it's for my part p inspection in a fortnight!
 
Good idea! Thanks Jason. PVC it is. Also what is the deal with removing the knockouts on the top of the CU to run cables off to final circuits with trunking butted up againt CU? Tails and main earth coming in the bottom in trunking, again butted up to CU. I know they are **** hot on IP4X rating. Do you think the method described would be acceptable to them?
 
Last edited by a moderator:
just butt trunking upto CU, you dont need to use knockouts if they are not practical, you canmake any hole, as long as you gromet it. I always use a little decorators caulk, to bead around trunking, where it enters boxes ect, just looks good IMO, and takes 10secs
 
Good idea! Thanks Jason. PVC it is. Also what is the deal with removing the knockouts on the top of the CU to run cables off to final circuits with trunking butted up againt CU? Tails and main earth coming in the bottom in trunking, again butted up to CU. I know they are **** hot on IP4X rating. Do you think the method described would be acceptable to them?

Please do not swear on the forums.
 
Tricky one this one, I have the same problem tomorrow, the old tails are run through the wall/cavity, if its a cavity how do you know whether there are any metal components in there, also in my case I am suspicious of the cable run and will find it hard to determine whether it meets the 50mm requirement. If it doesn't I assume it would need to be protected by an RCD if its not in the zones or less than 50mm away from the wall. If you were to use SWA you could take it into a galvanised box or trunking as has been said but this could look nasty in the room where the consumer unit is and you will have to gland it off at both ends of course. My solution for me is to use some PVC trunking and do it the best I can - it might not look great but at least you know you'll be complying with the regs. I unfortunately have a bit of a route to where the board is worst luck. Best of luck.
 
following a course at the I.E.T in london we were 'advised' not to change the meter tails if it is not necessary. If the system is already existing on say 16mm tails and you are not planning to overload what is already in place then why cause the hassle and cost to you and the customer of trying to change the tails? it is a waste of time and copper. also if you can prove by calculations that the main earths do not require changing, then don't (as long as bonding complies with being min. half that size etc.) If you do periodic inspections you will see where they are coming from, just because it doesn't comply with the new 17th regs doesn't make it unsafe. If it was done correctly to an older reg then it can still be safe and useable. but hey we all have to make our own minds up don't we......:D
 

Reply to meter tails in cavity wall in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
706
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
3K

Similar threads

  • Question
Thanks for the replies, I appreciate it.
Replies
4
Views
745

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top