Hi all,
Just doing a newbuild where the DB will be about 8m from the cut out/meter box. 25mm tails run in conduit on the surface of the outside wall then direct through the wall to the DB inside the house. DNO have provided a (non-fused) isolator in the meter cupboard after their 100A cut out.
I feel the simplest way to keep tick all the boxes would be to put a 100A switch fuse next to the isolator. Can't fit it (possibly not allowed to?) in the meter cupboard, so would have to put another enclosure next door.
Customer is asking, based on both price and not wanting more boxes than necessary on his wall, why the DNO's fuse won't do the same job as my switch fuse. To be honest, he's building a brand new house so fifty quid for an enclosure and a switch fuse won't break the bank, but I'm struggling to come up with a good reason that he needs two identically-rated fuses next to eachother.
Any ideas, or could I just use the DNO's fuse and leave it with just the non-fused isolator?
Thanks.
Just doing a newbuild where the DB will be about 8m from the cut out/meter box. 25mm tails run in conduit on the surface of the outside wall then direct through the wall to the DB inside the house. DNO have provided a (non-fused) isolator in the meter cupboard after their 100A cut out.
I feel the simplest way to keep tick all the boxes would be to put a 100A switch fuse next to the isolator. Can't fit it (possibly not allowed to?) in the meter cupboard, so would have to put another enclosure next door.
Customer is asking, based on both price and not wanting more boxes than necessary on his wall, why the DNO's fuse won't do the same job as my switch fuse. To be honest, he's building a brand new house so fifty quid for an enclosure and a switch fuse won't break the bank, but I'm struggling to come up with a good reason that he needs two identically-rated fuses next to eachother.
Any ideas, or could I just use the DNO's fuse and leave it with just the non-fused isolator?
Thanks.