Re: School Science block
That's exactly why I asked in post#3.
Your 50mm earth and main protective bonding are sized from the SUPPLIERS neutral on a PME system and 50mm is the largest given in table 54.8 (although these are minimum sizes).
We have on discussion now agreed the following specification but are still awaiting a confirmation from relevent bodys.
2 x Parallel 95mm on each phase
2 x Parallel 95mm on Neutral
From Reading table 54.8 bs 7671(20011)
The Main Earth & the bonding are both 50mm or is there a strange PME ruling increasing my main earth.
Unless any of you clever bods out there disagree??
We are already applying some diversity as we have 11 hobs, 11 ovens + sockets for kettles etc + ac & lighting maximum load could be 90+ amps per phase
We have supplied them from our panel board with 80amps per phase 80A tp mccb supplying a 25mm swa sub main & a 100amp 12tp way distboard. So hope they dont try everything at once.
That's exactly why I asked in post#3.
Your 50mm earth and main protective bonding are sized from the SUPPLIERS neutral on a PME system and 50mm is the largest given in table 54.8 (although these are minimum sizes).