MFT shows 235V, Drummond tester says dead, no live present | Page 2 | on ElectriciansForums

Discuss MFT shows 235V, Drummond tester says dead, no live present in the UK Electrical Forum area at ElectriciansForums.net

T

The Ghost

Attended call out at shop. Freezers, chillers and tills were down. Using MFT on V. measurement got 235V plugged into socket. Tested inside socket at terminals with drummond tester, nothing 0 V. Switched MFT to Loop and the neutral was missing. Just a bit puzzled why the MFT shows V. and Drummond 0 V. The neutrals in the neutral block had cooked away, loose neutrals and so on. I would post a pic but the forum does not allow me to post any pics any more.
 
interesting...... soon as i've had my breakfast smoke to kick-start the old lungs, going to have to connect 1553 to a socket with the N dissed.see what it says. no animals will be hurt during the course of the experiment.
 
an approved 2 probe voltage tester which indicates voltage even if only one conductor is present.
This is wrong and a dangerous misunderstanding.
If only one conductor is present then by definition there is no voltage present. The only tester that only needs one pole is a volt stick and we all know about them.
You can test between all conductors in an accessory as no volts and still have a dangerous voltage present. This would be especially likely in a light switch without earth and looped at the rose.
If you want to test you really need to test against all terminals and all exposed metallic items in t vicinity. Imagine touching an earthed radiator at the same time as a live light switch.
 
This is wrong and a dangerous misunderstanding.
If only one conductor is present then by definition there is no voltage present. The only tester that only needs one pole is a volt stick and we all know about them.
You can test between all conductors in an accessory as no volts and still have a dangerous voltage present. This would be especially likely in a light switch without earth and looped at the rose.
If you want to test you really need to test against all terminals and all exposed metallic items in t vicinity. Imagine touching an earthed radiator at the same time as a live light switch.
suppose that beats the wet finger.
 
You can test between all conductors in an accessory as no volts and still have a dangerous voltage present.
And this is why I use and carry a voltstick as a double-check, as it is not always practical to run a flylead to a trustworthy source of earth reference. One lead of a DMM with the other one dangling free, capacitively coupled to the outside world, will also often indicate this situation.
 

Reply to MFT shows 235V, Drummond tester says dead, no live present in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
303
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
818
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
884

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top