Been to a quote for a job this morning. Customer has just bought the house and wanted me to quote to replace/move an old fuse board as there were 2 in the house.

On looking at the job it appears that the old unit in the kitchen is being fed from the newer unit under the stairs in MICC/Pyro, the install date on the newer board is 2011 so don't know why the original spark did not just replace it at the time.

Told the customer I will need to do a full eicr to see what needs doing in the rest of the property but the old board will need removing (which he understands) and I would need to trace the circuits to see how I can best get them back to the main board.
As there is no labelling on either board I have suggested he plays flick the switch and makes a list of which mcb switches what off to save a bit of time when I return.

I have never had the ‘pleasure’ of working with micc as I only do domestic work so my question is do I need to take any precautions when I rip it all out?

20190615_100312.jpg


20190615_100202.jpg
 
considered it a sub board and you going to up grade it to a metal board to 18th ,you need to find what I is it feeding .and of course is the sub tails to it .
you could use the existing micc ,has long has all test carried out .
just to add looking at the main board some of the mcbs are not marked up .
 
Last edited:
The outer dome cap is sealing the cable to the gland body. Below it is an olive which compresses to the cable sheath when the dome cap is tightened. Releasing this should free the cable from the gland body, this is not an ideal thing to do once the olive is bedded to the sheath and body but needs must if you are not replacing the gland. You should then be able to free the gland without twisting the cable which you need to avoid at all costs. Some have earth tail pots fitted to the cable for earthing purposes if not I would probably fit an earthing nut, it looks metric from the dome cap which I can see a 2 written on it.
The dome cap will denote the cable size, 2H 2.5 means heavy duty two core, 2.5mm. 2L 2.5 means light duty two core, 2.5mm.
 
if you are ripping out the micc then no precautions necessary

if you are going to re-use the micc feed then don't cut the gland off otherwise you will be in a right old pickle
 
Its Metric 2L2.5 and would be no problem to re-gland.

Edit; although it has no earth tail. i'd be interested like 123 has said how they have terminated it into the plastic CU.
 
I have never had the ‘pleasure’ of working with micc

Not sure why the quotes. It's about the only cable I enjoy installing these days.

But wait, that copper covered stuff at the right hand end of the new board isn't MICC. Or if it is, it's gas MICC.
 
if only we could see a picture with the lid shut we could inspect the gland

rarely see orange micc in houses these days , see a bit of bare micc on my travels but rarely orange
 
T'other end is plastic though, and could be amusing. But if it's being axed, or even hammered, not terribly important.
 
I think the Op needs to come back and confirm the MICC is being removed and the circuits from the sub board are being extended to reach the main one.

No precautions except don’t snort the white powder
 
Intention will be to rip it out and take everything back to the main consumer unit, just need to work out what they all feed and if I can arrange the circuits to fit them in, there are 3 spare ways in new board, 4 breakers in old unit but covers not been off yet and nothing is labeled except the shower circuit.
As far as the termination in the newer board goes, they have drilled a small hole and fed the micc through it, no idea if they have glanded it inside.
 
Intention will be to rip it out and take everything back to the main consumer unit, just need to work out what they all feed and if I can arrange the circuits to fit them in, there are 3 spare ways in new board, 4 breakers in old unit but covers not been off yet and nothing is labeled except the shower circuit.
As far as the termination in the newer board goes, they have drilled a small hole and fed the micc through it, no idea if they have glanded it inside.

I wonder if they fed the original gland through a 20mm hole
 
Or put it through the hole, stripped it back and never bothered with a pot or gland, may be seen that a few times

Yeah, I've seen that too, sleeved and taped only....With a jubilee around the copper clad to clamp a cpc to!!.... Also seen many in control panels where multiple multi core pyro's brought in through same hole and then pots only fitted........There were some rough old boys out there too back in the day lol

I'm quite a fan of MICC and do enjoy when I get to work with it.
 
Yeah, I've seen that too, sleeved and taped only....With a jubilee around the copper clad to clamp a cpc to!!.... Also seen many in control panels where multiple multi core pyro's brought in through same hole and then pots only fitted........There were some rough old boys out there too back in the day lol
Nearly as bad as some of the rough young boys of today!!!!!!!
 
The number of swa lash ups these days has gone through the roof.
It seems to be every other time I come across some. If they can't terminate the armour correctly it's slice a shroud because they've forgotten it.
I don't know about you, but I used to take pride in first fixing cables of all sorts, making sure they were clipped nice, entering the enclosure properly, nice an neat, now slap it in know matter, as long as it tests OK and it works, it will be OK, what has become of trafesmen and Women? all gone to pot, I know who I lay the blame on and you don't need me to explain that do you?
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Bacup, Lancashire
Website
https://hudnottelectric.com/
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)
Business Name
Hudnott Electric Ltd

Thread Information

Title
MICC/PYRO advice please
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
50
Unsolved
--

Advert

Thread statistics

Created
PJH2903,
Last reply from
ipf,
Replies
50
Views
9,390

Advert

Back
Top