View the thread, titled "min csa of live conductors" which is posted in UK Electrical Forum on Electricians Forums.
hello peeps,
I could do with some help. And i will greatly be appricated to egt the help.
What is the min CSA of live conductors suitable for CCC and voltage drop for the following:
a. 3kw, 230v water heater
b. 11kw, 400v MIG welder
c. 12kw, 400v three phase machine
d. 5kw, 400v three phase machine
thanks you in advance for your help
so ive came to the conclusion that for a a 2.5mm would be suitable! ive now worked out vd which is 3.51v but not sure how to work out if its within the limits
cheque book and pen shall be yours..... (tag line from blankety blank (you were right)
Your supply voltage is 230V your volatge drop is 3.15V
3.15/230*100=1.36% is this less than the minimum %age drop?
so in this situation were we above the limit does this mean we have to select the next size cable up!
also just for the others above. were they a 400v supply needed does this mean they can only be supplied via 3 phase
Paul, how many more questions to this paper? Just to let people know.
hi,
the pages and pages of more questions. i know quite alot of it. but when i get helped like on this thread its fantastic as i now know all about the csa and working out cable sizes with ref to ccc and VD so cant thank you guys enough!
Am i okay with posting more question if i get stuck? they is bound to be a few more!
thanks
Reply to the thread, titled "min csa of live conductors" which is posted in UK Electrical Forum on Electricians Forums.