Afternoon all,
Just trying to clear something up, going through regs book at present.
Basically have got a TNC-S/PME installation, 16mm tails, 60/80a main fuse (think it is 60A), 6mm bonding to water and 6mm coming from service head to block then into CU as main earth.
Am I right that being as it is PME I am obliged to upgrade bonding to 10mm as per table 54.8 and that the note about bonding must be not less than half size of CSA for main earth only applies to conditions other than PME.
Just wanted to be clear as that's how I'm reading it, the job is a mains change. Thanks in advance.