Minimum protective conductor size | on ElectriciansForums

Discuss Minimum protective conductor size in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Tuttle

-
Arms
Joined
Feb 27, 2011
Messages
336
Reaction score
74
Location
Berkshire
CU replacement ... existing ring mains (on 30A 3036 fuses) are wired in 2.5mm T&E with a 1.0mm cpc :sad_smile:

I'm looking at Table B7 in the OSG which seems to say to me that the minimum protective conductor size is 1.5mm for a fault level up to 3kA on a class 3, 32A breaker.

I've got a max prospective fault current of 1.04kA at the origin, which is a fair amount less than 3kA.

How do I tell if this 2.5mm/1.0mm cable is ok on a 32A Type B RCBO?

I tried to use the adiabatic but couldn't work out what the disconnection time / let-through energy of the RCBO would be.
 
measure your PEFC (or calculate from Zs) at the furthest socket. from that use time/curreng graphs to determine the disconnection time of the MCB. then use that time in the adiabatic.
 
You are looking a it too deep mate. Yes you can do the adiabatic equation, but stick to standardisation. Your 2.5mm/1.0mm is fine. It will withstand the fault current up until disconnection. With a PEFC of 1.04kA, you disconnection will be almost instant.

Cheers..........Howard
 
measure your PEFC (or calculate from Zs) at the furthest socket. from that use time/curreng graphs to determine the disconnection time of the MCB. then use that time in the adiabatic.

Ok, so I've got Zs = 0.66 at socket outlets, which gives me a PEFC of 348A.

Looking at the characteristic of a 32A BS EN 61009 RCBO in the regs (Fig 3A4), the curve turns into a vertical line at 160A and there is a note that says refer to the manufacturer's let-through energy data for prospective fault currents in excess of those providing instantaneous operation, but I haven't found the manufactures info yet.

I realise that this is probably ok, and certainly better than it was on a 3036, but I would like to be able to justify why it is ok.
 
Ok, so I've got Zs = 0.66 at socket outlets, which gives me a PEFC of 348A.

Looking at the characteristic of a 32A BS EN 61009 RCBO in the regs (Fig 3A4), the curve turns into a vertical line at 160A and there is a note that says refer to the manufacturer's let-through energy data for prospective fault currents in excess of those providing instantaneous operation, but I haven't found the manufactures info yet.

I realise that this is probably ok, and certainly better than it was on a 3036, but I would like to be able to justify why it is ok.

348? Sure?
 
If you undertake the adiabatic calculation using 348A and a disconnection time of 0.1sec (it will be quicker than this in reality so the resultant csa will be high)
you get a csa of 0.95mm2 therefore this cable will be OK.
 
You obviously think I'm wrong, so no I'm not sure :wink_smile:

I'm thinking 230/0.66 = 348A

Is that not PEFC at the socket?

no not at all, just checking, it sounded right but I couldn't remember the formula and was hoping you would confirm that was all, nothing else really, apologies if you thought I was trying to confuse you.
 
I found some info on Hager breakers, which is too long to read on a Fri night ...

http://www.google.co.uk/url?sa=t&rc...kc8iNi_FGSyO_TQ&bvm=bv.43828540,d.d2k&cad=rja

From a quick search of this doc, Table 34 seems to say: MCB total let-through energy for a 32A MCB and a PSCC of 3kA is is 11kA[SUP]2[/SUP]S

So I'm thinking that I can plug this straight into the adiabatic equation as I[SUP]2[/SUP]t, which gives S = 0.91mm[SUP]2
[/SUP]
So I think that I'm alright which ever way I look at it, unless someone can tell me differently
 
I always thought that 1mm CPC on old 2.5 T&E was only a problem with rewirable fuses (BS3036). The max Zs tables in the OSG show that this is acceptable for up to 20A but not permitted for 30A rewirables. I was taught that a quick solution is a plug-in breaker.

As the OP points out, the Green OSG has a table (B7, page 120) which states that with BS60898 or 61009 devices, 1mm CPC is only acceptable for up to 16A, type B, with max 3kA fault current. For over 16A or a type C, the min CPC is 1.5mm. With fault current between 3 & 6 kA, min CPC is 2.5mm. Some figures given in this appendix are subject to the adiabatic, but not these.

This table was not in the original Red OSG but was on the Errata sheet issued by the IET in 2008.
 
Another factor to consider is that this is a ring, so there are two 1.0mm cpcs. I assume that the table in the OSG is for radials so assumes a single 1.5mm cpc. Not sure how much this helps though in a fault situation, especially if the fault is near to the origin on one leg of the ring.
 

Reply to Minimum protective conductor size in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Sticky
  • Article
Wicked I've just actually looked through it and it's very smart. Some good stuff in it. There's a tile association company that do a magazine...
Replies
2
Views
315
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
295
  • Article
Hi everyone, Another weekend, another sale! Get ready for colder days with Haverland Radiators, combining efficiency with modern design. Keep...
Replies
0
Views
361

Similar threads

  • Question
BS3871 type 3's have a similar shaped operating curve to BS60898 type C's. Any fault that will meet the disconnection time of 5s (for 63A...
Replies
5
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top