CU replacement ... existing ring mains (on 30A 3036 fuses) are wired in 2.5mm T&E with a 1.0mm cpc :sad_smile:
I'm looking at Table B7 in the OSG which seems to say to me that the minimum protective conductor size is 1.5mm for a fault level up to 3kA on a class 3, 32A breaker.
I've got a max prospective fault current of 1.04kA at the origin, which is a fair amount less than 3kA.
How do I tell if this 2.5mm/1.0mm cable is ok on a 32A Type B RCBO?
I tried to use the adiabatic but couldn't work out what the disconnection time / let-through energy of the RCBO would be.
I'm looking at Table B7 in the OSG which seems to say to me that the minimum protective conductor size is 1.5mm for a fault level up to 3kA on a class 3, 32A breaker.
I've got a max prospective fault current of 1.04kA at the origin, which is a fair amount less than 3kA.
How do I tell if this 2.5mm/1.0mm cable is ok on a 32A Type B RCBO?
I tried to use the adiabatic but couldn't work out what the disconnection time / let-through energy of the RCBO would be.