Minor Electrical Form filling | on ElectriciansForums

Discuss Minor Electrical Form filling in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

E

easysushi

Gents,

Quick question just to clarify.

When fillinging out Minor Works Cert. Part 3 Essential tests

3. Earth fault Loop Impedance

Is that taken at origin or at the socket that has just been installed. :confused:

Also the RCD tests is it the highest ms value recorded or lowest. :confused:
I'm quite sure its the highest

I know that these are all things I should know, and I do but got my assement next week and I'm just checking jobs that I have done and making sure all parperwork is good

Cheers


Ty
 
Gents,

Quick question just to clarify.

When fillinging out Minor Works Cert. Part 3 Essential tests

3. Earth fault Loop Impedance

Is that taken at origin or at the socket that has just been installed. :confused:

Also the RCD tests is it the highest ms value recorded or lowest. :confused:
I'm quite sure its the highest

I know that these are all things I should know, and I do but got my assement next week and I'm just checking jobs that I have done and making sure all parperwork is good

Cheers


Ty

Zs at all sockets including the ones installed and with both sockets and RCD record the highest




Chris
 

Reply to Minor Electrical Form filling in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
279
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
776
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
789

Similar threads

I usually put something like this To assess compliance with BS7671 for continued safe operation (5 year periodical inspection)
Replies
8
Views
440
Having some issues with my companys fluke 1662/1663 tester. Zeroing 2 leads for continuity test we get the value 0.08 which is expected. The issue...
Replies
0
Views
257

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top