Went to a property and found Zs on cooker circuit to be 240 ohms (TT by the way), installed new earth rod and got it down to 86 ohms. Minor works or Elec' Install cert'?
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss Minor or Electrical install cert'? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
Went to a property and found Zs on cooker circuit to be 240 ohms (TT by the way), installed new earth rod and got it down to 86 ohms. Minor works or Elec' Install cert'?
but, is replacing a dodgy rod an upgrade or a repair?
ALL circuits would be reqiured to have 30mA RCD protection, so the 100mA RCD would be redundant.Hi,
Minor works cert. will be ok, its not a special location or installing a new circuit.
Max. allowed reading on a TT earth rod is up to 200ohms.
Earth fault protection would be provided by 100ma TD RCD as main switch, Zs readings are not applicable to TT systems.
30ma RCBO/RCD would be required for majority of circuits if install was to 17th edition, which would be unlikely as most TT earthing is now changed to PME. 100ma would still be required for main switch on TT
Zs readings are not applicable to TT systems.