You would still need earth fault protection for any circuits that were not protected by 30ma RCBO/RCD.

Lenny, can you be a bit more specific, not sure what you mean.
 
30ma RCBO/RCD would be required for majority of circuits if install was to 17th edition, which would be unlikely as most TT earthing is now changed to PME. 100ma would still be required for main switch on TT

IF you install a dual RCD board then a 100ma RCD is not required as all circuits would be protected by a 30ma RCD ,TT systems are still in use and will not change in a large numer of rural area's , also there is a large amount of installations where a TNCS system is not permited ,and a Zs test is applicable for TT systems ,think you'll find that method 2 is a loop test Zs test is also carried out if you dont do a Zs test how will you know if the readings are less 200 ohms
 
Last edited by a moderator:
What if your customer wanted a dedicated circuit for a freezer or pc server etc.. without 30ma protection

Why would take a Zs reading if your Ze was 200ohm
 
What if your customer wanted a dedicated circuit for a freezer or pc server etc.. without 30ma protection

You are extreemly unlikely to get any TT system with a low enough Zs to rely on overcurrent and not need a 30m/amp Rcd
 
If you circuit with Ra reading of 200 ohms as you have stated which is done by method 2 zs no RCD protection then you have installed the circuit say 20 meters away then the resistance would increase causing the Zs to be higher than 200 ohms the circuit then could become unstable , the max reading of 200 ohms is for the earth rod not the installation , if you use an RCD at 30 ma then the max Zs of the installation would be 1667 ohms 100ma RCD 500 ohms . but where an over protective device is used the and equation of ZsxIa < Uo should be if im not mistaken
 
Think your getting confused with Ze & Zs.
Ze is the external earth fault loop impedance
Zs is measured at all final circuits that have ADS as a protective measure, to ensure protective devices will disconnect in required time. If Ze is higher than max Zs for device, RCD protection is required
 
If Ze is higher than max Zs for device, RCD protection is required

You suggested earlier that a TT system could have an rcd omited for a freezer,you then made the statement above

Given that you will not get a low enough Zs on a TT system for an overcurrent device,what of that freezer with no Rcd protection you suggested
 
Think your getting confused with Ze & Zs.
Ze is the external earth fault loop impedance
Zs is measured at all final circuits that have ADS as a protective measure, to ensure protective devices will disconnect in required time. If Ze is higher than max Zs for device, RCD protection is required


Not getting confused at all , not sure how you worked that one out but i think youll find that the Zs = Ze + R1R2

and i think you 'll find that if the Ze is higher than the Zs its caused by parrallel earth paths and hence the reason we do R1R2 tests rather than just a Zs test ,if the Zs reading is higher than that permitted by BS7671 for that protective device then an RCD is an option but not nessesarily required there are other ways of recitifying the problem ie increasing the cpc size
 
Think your side-tracking from the original question.
If the Ze on your TT system was 200ohmn your Zs is going to be above max. for any protective device.
Ze can never be higher than Zs.
100ma TD RCD`S are used as main switch to discriminate with 30ma rcd`s for final circuits.
30ma rcd`s are only required for cables buried in plaster at depth of less than 50mm or special locations
 
Think your side-tracking from the original question.
If the Ze on your TT system was 200ohmn your Zs is going to be above max. for any protective device.
Ze can never be higher than Zs.
100ma TD RCD`S are used as main switch to discriminate with 30ma rcd`s for final circuits.
30ma rcd`s are only required for cables buried in plaster at depth of less than 50mm or special locations

Not what you said a minuit ago ,, you dont actually measure Ze on a TT system you measure the earth path to the rod RA which if you dont know what the reading is it then can be replaced with a Zs test Reg 411.5.3 with RCD protection
if you have a dual RCD board then there is no need for a 100ma main switch RCD
 
The measurement from earth electrode to live incomer is the external earth loop for a TT system , otherwise known as Ze.
Method 2 in NICCY handbook can be done with a standard loop impedance tester.
Do you mean high integrity board when you say dual RCD? If so there are circuits in these boards without 30ma rcd protection, so where do you get your earth fault protection from on a TT system
 
Just to clarify, Ra is the impedance of the consumer's electrode and earthing conductor, whichever method of measurement is used (EFLI or dedicated electrode tester).

Many times on a TT system you have a Zs reading at a final circuit measuring far less than Ra because of parallel paths from main protective bonding etc.
 
Think your side-tracking from the original question.
If the Ze on your TT system was 200ohmn your Zs is going to be above max. for any protective device.
Ze can never be higher than Zs.
100ma TD RCD`S are used as main switch to discriminate with 30ma rcd`s for final circuits.
30ma rcd`s are only required for cables buried in plaster at depth of less than 50mm or special locations

It is well-known that most circuits feeding 13A socket-outlets now require RCD protection but equally important are requirements for additional protection of wiring concealed in walls or partitions, which includes lighting circuits and their concealed switch wiring. This means that the vast majority of domestic circuits, power and lighting now require 30mA RCD protection.
There are also important requirements to minimise nuisance tripping and collateral risks due to a tripped RCD affecting other circuits, such as lighting.
Socket-outlets
Rule 411.3.3 calls for additional protection by means of a 30mA RCD for all socket-outlets with a rated current not exceeding 20A for use by “ordinary persons”. The only exceptions allowed are for socket-outlets for use under the supervision of skilled or instructed persons (e.g. some commercial/industrial locations) or a specifically labelled socket provided for connection of a particular item of equipment (such as a freezer).
This rule clearly covers the vast majority of domestic circuits feeding 13A socket-outlets, and any other socket-outlets (5A, 15A etc.) up to 20A. There is also a requirement for RCD protection of circuits feeding mobile equipment with a current rating up to 32A for use outdoors.
Cables in walls or partitions
Rule 522.6.7 calls for RCD protection of wiring concealed in walls or partitions. All concealed wiring at a depth of less than 50mm now requires protection by a 30mA RCD unless it is provided with earthed mechanical protection, for example by metallic conduit or trunking. This applies to many lighting circuits and their switch wiring, including those installed in previously defined a “Safe Zones”.
There is a further requirement for protection by means of a 30mA RCD where cables are concealed in walls constructed with metal stud partitions, irrespective of the depth from the surface, unless provided with protection in the form of earthed metallic covering, trunking, conduit or other mechanical protection so as to avoid damage to the cable during installation or construction of the wall.
Special locations
Rule 710.411.3.3 calls for RCD protection of all circuits in specific locations such as those containing a fixed bath or shower. This means that, in bathrooms or bedrooms with en-suite facilities, circuits feeding lighting, heating and showers must have RCD protection.
Other “special installations and locations” as defined in Part 7 of the Regulations are also required to have RCD protection. These include swimming pools and saunas, agricultural premises, caravans and caravan sites, floor and ceiling heating systems.
Sub-division of circuits
Rules 314.1 and 2 require that every installation should be divided into circuits as necessary to avoid danger and minimise inconvenience in the event of a fault. Designers are required to reduce the possibility of unwanted RCD tripping due to excessive protective conductor currents but not due to an earth fault.
Separate circuits may be required for parts of the installation which need to be separately controlled in such a way that they are not affected by the failure of other circuits. The appropriate subdivision should take account of any danger arising from the failure of a single circuit, for example an RCD trip causing the disconnection of an important lighting circuit.
This affects the configuration of the protective devices in a consumer unit. For example if a number of circuits are protected by a common 30mA RCD, lighting circuits need to be spread over more than one RCD.
Rules 314.1 & 2 also call upon the designer to take steps to reduce the likelihood of unwanted RCD tripping due to excessive protective conductor currents, other than earth faults.
Typical situations would include IT equipment with certain types of radio frequency interference suppression, and certain types of heating equipment. The cumulative effect of such loads can produce a standing earth leakage current that is beyond the threshold point of a normal 30mA RCD. However this situation is becoming more common in residential environments.
Earth loop impedance
It should also be noted that Chapter 41 of the Regulations includes revised earth loop impedance tables based on a nominal voltage of 230V (Previously 240V). This results in slightly lower values of earth loop impedance and could, in some situations, mean that RCDs will be required to achieve the required disconnection time where previously overcurrent protection devices would be considered adequate.
Solutions
A number of different consumer unit configurations are possible to satisfy these requirements. The ideal solution is an in-line arrangement with an RCBO (combined MCB and RCD) providing overcurrent and residual current protection of each final circuit; in this case tripping of an RCBO will not affect other circuits. However, this is also an expensive solution. The most economic solution is a dual-RCD unit with individual circuits protected by miniature circuit-breakers divided between two RCDs.
 
The measurement from earth electrode to live incomer is the external earth loop for a TT system , otherwise known as Ze.
Method 2 in NICCY handbook can be done with a standard loop impedance tester.
Do you mean high integrity board when you say dual RCD? If so there are circuits in these boards without 30ma rcd protection, so where do you get your earth fault protection from on a TT system



An RCBO
 

Reply to Minor or Electrical install cert'? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
299
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
810
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
857

Similar threads

Thank you all, yes I didn’t think they do and I have done minor works but the helpline was not very helpful. Got my yearly assessment soon so I...
Replies
4
Views
282
Unless the circuit is new or has recently been tested/certified by a.n.other, I'm not sure how you prove the circuit is 'safe' to connect to...
Replies
1
Views
250

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top