When connecting a new boiler into an existing switch fused connection unit and you are not modifying or extending any of the fixed circuit wiring, do you carry out the full range of tests shown on the minor works cert, with reference to a NICEIC version?
Zs @ db
R1R2 of the circuit up to the switch fuse
I/R test of the circuit before connecting the boiler
I/R test of the circuit when the boiler has been connected at a lower test voltage 250
Or would you just do a zs @ boiler and RCD tests etc?
 
Unless the circuit is new or has recently been tested/certified by a.n.other, I'm not sure how you prove the circuit is 'safe' to connect to without doing the full MW tests! (eg if R1+R2 or Zs) proved to be excessively high which could mean an unreliable earth connection which could fail in time, leaving the boiler with no earth return in the event of a fault with boiler casing raised to 230V!
 

Reply to Minor works but not a minor works? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
339
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
875
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Thank you all, yes I didn’t think they do and I have done minor works but the helpline was not very helpful. Got my yearly assessment soon so I...
Replies
4
Views
288
  • Question
If this is a genuine change then throw it back at them, a nicely worded email explaining the additional testing requirements and paperwork charge...
Replies
14
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top