Sussex1978

Hi all, some advice needed please - when changing a standard 2gang socket outlet to RCD protected 2gang socket would a minor works very be required.

Reading the regs it states that if a charchacteristics of a circuit change than it would, we are divided, I think not yet a mate thinks you should.

Views and advice please.... Mixed messages from niceic
 
Last edited by a moderator:
Hi all, some advice needed please - when changing a standard 2gang socket outlet to RCD protected 2gang socket would a minor works very be required.

Reading the regs it states that if a charchacteristics of a circuit change than it would, we are divided, I think not yet a mate thinks you should.

Views and advice please as niceic shut at 1630!!!!!!

"characteristics" meaning of resistance on the cable which you havnt altered its just a face plate
 
Personally I would for an RCD plate, just to show test results and that the device was working when fitted.
 
I agree that we should complete an RCD test but a full circuit test seems to be excessive too me esp as we've not changed the circuit other than replacing all be it with added protection
 
Also depends on the customer, landlords, rental agencies etc may want a record of when the work was carried out. Also insurance companies.
 
Personally I would for an RCD plate, just to show test results and that the device was working when fitted.

so you change a socket face plate for a rcd socket you test (THE SOCKET) issue a minor works certificate and notify building control through your respected body..................... Q, how much have you charged for this 2 min job £100
 
The paperwork would only be a record of test, no mention of LABC etc.
 
only need to notify LABC if socket outlet is in a kitchen, bathroom, or outside.
 
Why would you notify!!!! You're only replacing a socket plate with a better one.This would not affect the characteristics of said circuit.Providing you tighten the terminals etc. your Zs would give you the exact reading.I would install the new RCD socket and test accordingly NOTHING MORE.


Tin hat on!!!!!
 
Last edited:
you issue minorworks you have to notify read up on minor works cause changing a socket plate is classed as diy as is a light fitting
disagree . no need to notify LABC as it's not a new circuit. ( unless it's in a special location)
 
TABLE 1: WORK THAT DOES NOT NEED TO BE NOTIFIED TO BUILDING CONTROL
BODIES
Work consisting of:
• Replacing accessories such as socket-outlets, control switches and ceiling roses.
• Replacing the cable for a single circuit only, where damaged, for example, by fire, rodent or
impact (a).
• Re-fix or replacing the enclosures of existing installation components (b).
• Providing mechanical protection to existing fixed installations (c).
Work that is not in a kitchen or special location and does not involve special installation
and consists of:
• Adding lighting points (light fittings and switches) to an existing circuit (e).
• Adding socket-outlets and fused spurs to an existing ring or radial circuit.
• Installing or upgrading main or supplementary equipotential bonding (f).
Notes:
(a) On condition that the replacement cable has the same current carrying capacity, follows the same
route and does not serve more than one sub-circuit through a distribution board.
(b) If the circuit’s protective measures are unaffected.
(c) If the circuit’s protective measures and current-carrying capacity of conductors are unaffected by
increased thermal insulation.
(d) Special locations and installations are listed in Table 2.
(e) Only if the existing circuit protective device is suitable and provides protection for the modified circuit,
and other relevant safety provisions are satisfactory.
(f) Such work shall comply with other applicable legislation, such as the Gas Safety (Installation and
Use) Regulations.
TABLE 2: WORK THAT MUST BE NOTIFIED – SPECIAL LOCATIONS AND INSTALLATIONS
• Locations containing a bathtub or shower basin.
• Swimming pools or paddling pools.
• Hot air saunas.
• Electric floor or ceiling heating systems.
• Garden lighting or power installations.
• Solar photovoltaic (PV) power supply systems.
• Small scale generators such as MicroCHP units.
• Extra-low voltage lighting installations, other than pre-assembled, CE-marked lighting sets.

NO NEED TO NOTIFY!!!! You are only replacing an accessory.you're not changing the cable size or adding to an existing circuit.
 
Last edited:

Reply to Minor works cert question in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
361
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
917
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Unless the circuit is new or has recently been tested/certified by a.n.other, I'm not sure how you prove the circuit is 'safe' to connect to...
Replies
1
Views
273
  • Question
If this is a genuine change then throw it back at them, a nicely worded email explaining the additional testing requirements and paperwork charge...
Replies
14
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top