Billy Reid

Hi, had a mira sport 10.8 kw shower fitted 10 years ago and all new cable installed.
Just had a new mira 10.8 kw shower this week to replace old one. Just a case of swapping like for like.
Here's my question though. A bit of cable was left and it is 6mm. Mira says it needs to be 10mm?
Anyone help? I
Would have thought sparky fitting shower 10 years ago and fitting new cable would have used 10mm? Or was 6mm standard back then?
 
Thanks. I guessed it needed 10mm but don't understand why 10mm wasn't used when fitting original shower as all cable was replaced.
I'm not electricity minded and font know ow what 50a mob is though. Sorry.
Breaker switch is Wylex .has B40 on it and 3000.
Sorry don't know much. Guess I will have to find a sparky to rewire with 10mm .
 
Thanks. I guessed it needed 10mm but don't understand why 10mm wasn't used when fitting original shower as all cable was replaced.
I'm not electricity minded and font know ow what 50a mob is though. Sorry.
Breaker switch is Wylex .has B40 on it and 3000.
Sorry don't know much. Guess I will have to find a sparky to rewire with 10mm .


Cheaper to get a less powerful shower surely!

Does it really need to be 10.8Kw. Mine is 7.5Kw and still gets me nice and clean. :)
 
Was the first 10.8kw shower the original shower unit on that circuit was installed? Was there another shower unit before the 10.8kw? Is it easy to rewire. If not buy a smaller rated shower to suit your cable. Don't forget if installing a new circuit, an RCD will be required
 
Was the first 10.8kw shower the original shower unit on that circuit was installed? Was there another shower unit before the 10.8kw? Is it easy to rewire. If not buy a smaller rated shower to suit your cable. Don't forget if installing a new circuit, an RCD will be required

I had a shower before get to grips 10.8 fitted. Maybe 7.5 but had bathroom done up and chose 10.8 . Guy fitting the 10.8 said it would need new cable to facilitate the 10.8. Font know why he used 6mm though and wouldn't have found out either if we didn't replace shower.
The previous 10.8 shower has been running off 6mm for 10 years!!
 

Reply to mira sport 10.8 question in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
438
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

In the picture of the socket, it looks like one of the neutrals may have been screwed in over the insulation. Therefore, the live may also have...
    • Like
Replies
14
Views
818
  • Question
What is the distance from the point outside the house to the shed?
Replies
8
Views
792

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top