I have a brand new MK 63amp RCD that fails Ix5 test everything else tests fine on the board, I tested with all circuits off everything unplugged so swapped it for another thinking must have a faulty one but the same result, it will trip at 50ms and ramp tested at 33ma, ze=0.18 what could be happening? any advice on what could be wrong would be greatly appreciated.
 
domestic, unable to get in today but should on monday
 
There’s no requirement in the 18th edition for RCDs to trip in any particular time.

As for this testing with all loads disconnected, what’s that all about?
Yes Mrs Miggins, your RCD works fine, as long as you don’t switch anything on.

The note in 643.8 makes reference to compliance being achieved in terms of additional protection when the 40ms at 5x rating is met.
I just see that this information has migrated from section 415 and found a new home.
 
Yes, but it’s a note not a requirement.
The requirement now, is just to have 30mA RCD protection
The reg I quoted requires RCDs for additional protection to be tested to verify effectiveness.
The note defines the time that should be met to verify effectiveness.

If the time cannot be met then it could not be deemed effective and therefore not compliant ?

Just how I read it.
 
I have read this as well and I agree with @Andy78 the question is what can I do to improve the disconnection times I need a solution for the customer.
 
what size is the main earth and is the connection Ok? Is it TNS or what? I was just thinking to increase the main earth size or improve the earthing arrangement.
 
Last edited by a moderator:
16mm main earth, TNCS 10mm bonding to gas & water
 
Hi - perhaps confirm your tester is set to AC (I think these MK RCDs will be AC type, rather than A). If still no good, perhaps try a higher test current and see what happens. The reg now allows for more than 150mA to be applied to achieve less than 40ms. I don’t like it, but that’s what I understand.
 

Reply to MK 63amp RCD that fails Ix5 test everything else tests fine on the board in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Hope everyone has had a great Christmas and here’s hoping we all have a better new year coming our way ! Remember our riches aren’t measured by...
    • Friendly
    • Like
Replies
11
Views
591
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
772
  • Sticky
  • Article
Thanks so much for sharing this with us! I’ll definitely take a look, it seems like there are a lot of useful and interesting products. The idea...
    • Like
Replies
5
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top