How can I get a 3 wire no trip test of between 2ohms and 1114 ohms

But on a high current test get 0.19 between live and earth and 0.1 between live and neutral.

When the rcd is bridged out I can do the 3 wire test and get a sensible zs of 0.2 ohms.

The strangest part is the first 2 sockets on the circuit can be tested with the rcd in and they still give sensible zs readings....?
 
This is why it's always preferable to do a 2 wire high current test. I believe the 3 wire tests either uses a very low current so as not to trip the RCD or they do some fancy jiggery pokery to saturate the sense coil in the RCD to prevent it detecting the imbalance the test creates (and thus the RCD won't trip).

But... all of this means the reading is much less reliable than the 2 lead high current version. The fact it's so variable should also give you cause for concern and an indication of it's unreliable nature.

Different RCDs seem to have different effects and I have had issues testing through older MK RCDs myself.

Just remember if the readings are garbage you could take an R1+R2 measurement for the circuit, get the Ze for the board and use a calculated Zs (this is a perfectly acceptable means of verifying you meet the maximum Zs requirements).

Regarding the strangest part... have you tested every socket outlet with the RCD jumpered out? If not, I would probably do so as based on the strangest part it could be a bad connection. An R1+R2 test may find such a situation.
 

Reply to Mk 7860 uplift in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
380
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
957
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

In the 80's I was taught that with PME earthing arrangements we used 16mm for the main earthing conductor, some went a bit crazy and were bonding...
Replies
11
Views
2K
I was at the other end of the results spectrum today. As I was driving home I had a call from my "Mrs Richards from Fawlty Towers" lady, very deaf...
2
Replies
20
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top