No, is the short answer. It will fit in the board, on the DIN rail and be in line with the rest, however you'll have to bodge the busbar. When I've fitted new MK breakers to old MK boards, I've chopped out the busbar prong where the new breaker is to sit and linked from the main switch to it using a short length of 16mm/25mm single core cable depending on the main fuse rating.
 
As a side note, it doesnt have to be a 16/25mm cable, you can use the principle of backfusing to size the feed to the MCB. I ofetn have to do this, in old panels, if there is no busbar, and i need a new way creating. So if the MCB is a 32A, then id use at least 4mm2. To be honest i usually use a bit of 6mm if ive got it about. The next electrician should look at the board before he decides to lump a new breaker in and rely on your link.
 
As a side note, it doesnt have to be a 16/25mm cable, you can use the principle of backfusing to size the feed to the MCB.

I can see the idea there, I just don't like the idea of protecting a 4mm cable with a 100A main fuse. What happens if over time, the connection becomes loose for whatever reason, then that cable will start a fire long before the main fuse even realises what is going on! Whenever I change a CU I always carry out a free first check a year after installation and you'd be surprised how many times I've had to tighten really loose connections after only a year of use due to expansion/contraction of copper terminations when heated and cooled.

Like I said, I can see your logic, but I personally wouldn't feel comfortable doing it that way.
 

Reply to mk mcb in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
285
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
786
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
804

Similar threads

  • Question
The legs on the bus bar are too long for the new rcbos
Replies
3
Views
471
  • Article
The mcb used will be sized for the spd cable.
Replies
4
Views
429

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top