Hi all. Newbie please be gentle...

My daughter in law moved into a new [2007] build. All socket circuits 20A radial MCB. One socket circuit trips rcd intermittently when the Wi-Fi router psu plugged in. Psu is double insulated and pat tests ok. Radial tests out ok with 50M ohm at 500v. Nothing obvious in the socket backs. Any ideas what to look at next? I'm here for the day visiting. Thanks!
 

Attachments

  • [ElectriciansForums.net] Modern wiring help rcd trip
    20190817_091949.jpg
    1.1 MB · Views: 123
  • [ElectriciansForums.net] Modern wiring help rcd trip
    20190817_092335.jpg
    3 MB · Views: 375
Psu is double insulated and pat tests ok.

Did you test it yourself, i.e is the test trustworthy? I mention this because if it was someone else's test, I would double check it. A lot of numpty testers don't seem to connect the earth probe to the DC output connector when they 'test' small power supplies, so in fact they are not testing anything. It could have any amount of leakage or insulation failure from line to output but they wouldn't find it.

Actually, what happens if you power-up the PSU but don't connect the DC output to the actual router? Keep the plug out of contact with anything, so that there cannot be any earth leakage because the only connections are to L & N. If the RCD now doesn't trip, that suggests it is a leakage problem. If it trips, then you have something spooky going on.
 
Had a similar problem on a job myself recently and it may just be a coincidence that the RCD trips when the router is plugged in as the neutrals are common.
24mA is not too low for a 30mA RCD. You don't mention the 'half times' test, may indicate a faulty RCD.
Also no IR test results - Possible cable fault!
If the circuit tests satisfactorily, its possible the accumulated leakage current from all the RCD protected circuits exceeds 24mA.
 
So you whacked in a new rcd...which means you are now responsible for that circuit....or all the circuits on the rcd side....hope you have filled out an EIC or if anything goes wrong in that property you will be liable...not the landlord
 

Reply to Modern wiring help rcd trip in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
438
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

SOLVED Thanks for all the help. It was nothing to do with the smoke detector. In this new hole (where there will be a light fitting) three white...
    • Like
2
Replies
24
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top