Promised I'd show you all a photo sometime so here it is: our Rapid Response Panel Test Rig
We're still looking for reasonably priced USB connected meters, till then, this has to suffice:
![DSCF2621.jpg DSCF2621.jpg](https://electricians.s3.eu-west-1.amazonaws.com/data/attachments/4/4053-5f43efb5927a055896cd101afa6d0a67.jpg?hash=X0PvtZJ6BV)
In individual panel test mode, hook the two long leads up to the panel, the top (clamp) meter is set to read Volts, so gives us VoC, press the button, the bottom meter is a 20 Amp, (up to 60V DC) through meter, so we then get the instantaneous ISc, Scan the Panel Barcode into the spreadsheet, and manually enter the Irradiance meter reading, then next panel.
In String test mode, hook the two long leads up to the string MC4's (or adapters if SMA Sunnyclic), you need to swap the meters round as our clamp meter only reads up to 600V DC and the bottom meter won't take >60V DC in direct current mode, however it will read up to 1000V DC!
So connect the bottom meter up to the Voc connectors, disconnect the clamp meter and put it round one of the long cables, and there you go, a one handed string test meter setup.
It may not be worthwhile doing the latter bit if you've only got a couple of strings, however when you've got 15 of them at 840V a time, it's a safer way!