ive installed a new shower circuit, so i do a full sequence of tests for the new circuit and put them on a electrical installation certificate.........


Q1. do i fill in the inspection sheets as i would if it was an initial verification, also completing the particulars at the origin,and also doing all ze, pfc tests, continuity of main bonding conductors ect....

Q2. the consumer unit has a 100a main switch, a 63a main rcd and another 63a rcd, the shower is on a 50a breaker, so do i need to carry out an rcd test on the shower even tho its not directly connected to an rcd:confused:
any advice muchos gracias

more questions may follow!!!!
 
an electrical installation certificate is required for a new installation, an addition, or an alteration. as your installation work constitues an addition it clearly needs a full electrical installation certificate.
 
with regard to your shower, it MUST have an rcd or rcbo giving additional protection. the rcd already fitted has only got to be tested on any one circuit as the results will apply equally to all the circuits protectd by the rcd
 
ive installed a new shower circuit, so i do a full sequence of tests for the new circuit and put them on a electrical installation certificate.........


Q1. do i fill in the inspection sheets as i would if it was an initial verification, also completing the particulars at the origin,and also doing all ze, pfc tests, continuity of main bonding conductors ect....Yes.

Q2. the consumer unit has a 100a main switch, a 63a main rcd and another 63a rcd, the shower is on a 50a breaker, so do i need to carry out an rcd test on the shower even tho its not directly connected to an rcd:confused: Sounds like a dual RCD CU you have there, so the shower MCB will be protected by one of these RCD's (if not then it should be!!)
any advice muchos gracias

more questions may follow!!!!

GN3 has guidance on insp and testing, what is needed and when etc.
 

Reply to more questions on test certificates in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
279
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
776
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
789

Similar threads

Interesting question & always gonna get different views on this. EICR testing seems to have changed over the years & not by us the Electricians...
Replies
7
Views
1K
  • Question
Tim - shear brilliance mate
Replies
12
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top