Evening all...

I'm in two minds whether to post this but i've thought about it for a while and was hopeing someone could give me a very clear idea of how they would find the fault.

Lets say we have a ring. We test between N-E at the CU and find a poor IR reading, lets say 0Mohms, ie socket screw has gone through the neutral.

I break the ring somewhere in the house and then test both neutrals to see which side the fault is on.

I then break the ring between the CU and the already broken point (on the fault side) etc etc until I have found the fault.

This sounds very straight forward, but in practise it can be very difficult to know which sockets/FCU are actually on the faulty side once you have broken the ring as you have to completely guess at the layout of the ring.

The only way I could think of doing it would be to have a good idea of where all the sockets fed by the ring are in the first place, then break the ring, find the faulty side and then reconnect just the faulty side in the CU so that you know that any socket that is dead is not on the faulty side and can be discounted. Any socket that is live could be the culprit, and slowly break it down this way which will also give you a bit of a picture of the layout of the ring.

How do others do this?

Cheers..
I always think the Murray loop test is the simplest and quickest test to locate a fault. :)
 
Half Split Method...

(This is from general fault finding on equipments)

Unless a fault is a usual suspect (which can lead you down a wrong path if you're not careful) always try and work methodically. Narrow down on a 50-50 basis unless there are reasons to say otherwise. Often these reasonings will be gut from experience but usually they will be deduced.

But first, check the ffing fuses.
 
Hi all
did have a problem on some ground lights outside years ago friend of mine I was helping for the day, we started making resin kits up splitting cable down the drive ( a long way) about 20 joints total split cable terminate join light cable anyway on the next day it was being back filled & Mike was testing when he found N/E fault on IR test, found fault quite quick by doing r1 r2 at each light starting at beginning working his way Down readings started going down till go to low place then started from other end got the same low reading at that point, dug back up & hey presto that was the one cut in new joint bigger swa kit job done.
Could work on ring disconnect from DB join ends & go round do a r1-r2 looking for lowest reading at one point or between 2, split legs at board & repeat process, should have a low reading at one or two points, this way no sockets off can be done in any combination l/n n/e. On continuity for obvious reasons not IR, low ohms should do the trick, just a thought
 
Hi all
did have a problem on some ground lights outside years ago friend of mine I was helping for the day, we started making resin kits up splitting cable down the drive ( a long way) about 20 joints total split cable terminate join light cable anyway on the next day it was being back filled & Mike was testing when he found N/E fault on IR test, found fault quite quick by doing r1 r2 at each light starting at beginning working his way Down readings started going down till go to low place then started from other end got the same low reading at that point, dug back up & hey presto that was the one cut in new joint bigger swa kit job done.
Could work on ring disconnect from DB join ends & go round do a r1-r2 looking for lowest reading at one point or between 2, split legs at board & repeat process, should have a low reading at one or two points, this way no sockets off can be done in any combination l/n n/e. On continuity for obvious reasons not IR, low ohms should do the trick, just a thought
on ring.

link N1-E1 and L2-E2 at board

then go to where you think the middle is then check continuity on n-e and l-e this will tell you which leg is down.

connect it back up and pick another socket but remember the last resistance value, some people dont install rings the way you think.

me and a mate had a nightmare trying to find a fault on a ring circuit becauss of the way the ring was wired, split the ring in half and 1/2 came on in each room with some still off.

had to resort to drawing it out where we though ring went while trying to split it and work upto fault
 
Hi shanky
what I meant was you don't need to know the middle you are looking for the lowest reading on the ring on any of the pairs or between the pairs, this could be fault location, ie if you had say 20,19,17,45,19,0.1, 21 ect then surely lowest reading could be location of fault on low continuity, forget it being a ring just look for the lowest reading, no sockets of no split only at board just to check split legs at board & go round again if same location lowest reading should be the fault. Just a thought without splitting down the ring straight away, next time I get call for similar fault I will give it a quick go should only take 15 mins depending on size of ring
 
Hi shanky
what I meant was you don't need to know the middle you are looking for the lowest reading on the ring on any of the pairs or between the pairs, this could be fault location, ie if you had say 20,19,17,45,19,0.1, 21 ect then surely lowest reading could be location of fault on low continuity, forget it being a ring just look for the lowest reading, no sockets of no split only at board just to check split legs at board & go round again if same location lowest reading should be the fault. Just a thought without splitting down the ring straight away, next time I get call for similar fault I will give it a quick go should only take 15 mins depending on size of ring

That works when you have a low impedance fault such as a short. the lowest reading obtained will be closest to the fault. For insulation faults in M/Ohm range it wont be accurate enough and will show the same reading throughout the circuit.
 
Hi that's what I meant if the fault was low enough it could show easy to check if it shows up on a continuity check at board then should be able to use it to find it, if it is to high then I would agree it won't work & would have to user IR testing.
 

Reply to Most effective or correct way to fault find? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
527
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
982
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
916

Similar threads

Very technical :D
    • Like
Replies
9
Views
563
Seen this where T&E has been fixed with a flat bend of too tight a radius.
2 3
Replies
35
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top