Some things are a little puzzling. Ventilation, i.e. a Fan is not usually the most demanding of starts. . Again cannot imagine this motor is starting and stopping every minute or so, which should not really be hamering the VSD. I would check the motor windings first - oh and the bearings, could be totally coincidental.
 
If your motor is cooking and now burnt that would explain why it has trouble starting.
 
It may be the case the OP has come across a duel voltage motor which was correctly connected for star 400v (OP then connected in delta been 230v).. in doing so its possible the motor ran ok for a few weeks due to the settings on the inverter not been full speed as frequency and voltage rise as speed demand rises so it may be the case the inverter wasn't supplying full voltage letting the overvoltaged winding last longer but inevitably they have overheated and been damaged.

@ silva fox .... your inverter listing is out dated, ive fitted 110v single ph to 230v 3ph recently; yes agree sounds mind boggling how its achieved but i tell thee no lies :)
 
... @ silva foxx .... your inverter listing is out dated, ive fitted 110v single ph to 230v 3ph recently; yes agree sounds mind boggling how its achieved but i tell thee no lies :)

AC Inverter Drives (115V)

As said in post #14... Everyday is a school day.

Not surprised to learn of that... the amount of 1ph dual voltage equipment we have at hand where you have that little red slide toggle to choose 120 or 240 as input voltage.
 
I had a similar one to this yesterday, 11 kw was wired in star delta and we were putting a VSD on it. Nothing on the plate about wether it would run in star or delta. Possibly naively i assumed delta for the size of the motor but it wouldn't run. Changed it to star and run a treat.

Is there any particular rule for sizes of motor and star or delta ?
 
Think you need to review the motors sticky we have on this forum and understand the the different methods of connection to single voltage, duel voltage motors.... doing what you are doing will be a costly lesson to learn, connecting the motor up correctly is crucial and just because it runs dosn't mean you got it correct, an incorrect connection can overvoltage the windings, reduce the torque by a factor of 3 etc etc but many variables can mask the issue like VSD speed settings etc.
I wouldn't in your shoes be venturing down this avenue until you understand motors a little more.. please take as constructive advice :)
 
I had a similar one to this yesterday, 11 kw was wired in star delta and we were putting a VSD on it. Nothing on the plate about wether it would run in star or delta. Possibly naively i assumed delta for the size of the motor but it wouldn't run. Changed it to star and run a treat.

Is there any particular rule for sizes of motor and star or delta ?

Unfortunately no. This is why the lads have asked for the motor plate details. I covered motor voltages in the motor section, it may take a bit of finding, nothing is in order.
 
On certain invertors you have to program in the nameplate details. If you program in that the motor is star and it is actually connected delta have seen before that the motor struggles to run.
 
On certain invertors you have to program in the nameplate details. If you program in that the motor is star and it is actually connected delta have seen before that the motor struggles to run.
Yes agree with the motor nameplate values but i yet to have an inverter ask if star or delta, as motor configerations vary this wouldn't be any use to the inverter, its up to the engineer/electrician to ensure output voltage matches winding configeration.
690 Y --- 400v D
400 Y --- 230v D
2 common duel voltage motors from different parts of the world but require the opposite connection for 400v.
 

Reply to the thread, titled "Motor connected in star not delta" which is posted in Commercial Electrical Advice on Electricians Forums.

Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Daily, weekly or monthly email

Back
Top