toland96

lookin for advice on a problem which may come up (or may not), i have 2 motors on one common shaft 1 duty 1 standby driving a fan, these motors are VSD driven, i have 2no 3phase supplies to the VSDs (Not through contactors) 1 volt free enable for both duty and standby VSD's and 2 seperate 0-10vdc signals to VSD's, question: if i enable the duty fan (this will also rotate the Standby motor) will any voltage be back fed throught the standby windings due to it rotating? If so would this damage the VSD or cause interference to the supply feeding the standby VSD? or am i just an idiot? I havent allot of experience in this feild and would appreciate any help
 
Think it depends on the motor really if the motor has permanent magnets in it then turning the shaft will induce a current into the windings and back up the supply cables but if its say like a dc motor with a seperate armature windings and field windings then no as the magnetic flux is created by the power to these seperate windings.
 
We do this all the time with no problems or damage to the inverter at all. You will need to set the inverter up for "Flying Start" not "Ramping".
the motors should not cause interference if, silflex cable has been used from the inverter to the motor and grounded both ends
 
We do this all the time with no problems or damage to the inverter at all. You will need to set the inverter up for "Flying Start" not "Ramping".
the motors should not cause interference if, silflex cable has been used from the inverter to the motor and grounded both ends
Still wonder as most inverters do state never to put power to the out going terminals in big bold writing i would be inclined to contact tech in this case, again this is only an issue if the motor by design would act as a generator when mechanical energy is applied to turn it. As he hasnt specified the motor or drive its hard to say.
 
Last edited:
Worked grand only small voltage feed back, put delay on changeover as i didnt have the days it takes to read/view the VSD manual/CD Manual to work out which menu/sub menu/sub sub menu/sub sub sub menu you would find the flying start option, lol , appreciate the help tho, cheers
 

Reply to Motor Help Please in the Electrician Talk | All Countries area at ElectriciansForums.net

Similar Threads

  • Question
It's the video link I've posted above. - (Initial verication testing someone else's crap work) Cheers
Replies
46
Views
13K
T
  • Question
The issue I've had with WPD on a couple of occassions is where there is minimal or no evidence of a "proper" (e.g. sweated on) earth connection to...
    • Like
    • Winner
    • Useful
Replies
7
Views
2K
G
How many phase is your Mercury Arc Rectifier by the way Lucien and what type of equipment would you need to give it a PAT test I wonder ? I gather...
Replies
20
Views
5K
goodconnection
G
H
  • Question
Welcome to the forum. I've made your post into a new thread for you although I'm not sure you'll get your answer here, this is a general...
Replies
1
Views
2K
K
  • Question
Closed by request
2 3 4 5
Replies
110
Views
9K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks