Contactor coil on manual star delta starter has burned out due to possible humidity and old age.
The easiest solution was to find a replacement coil, only thing is it's quite ancient so finding a similar size coil is nearly impossible.
Since it's a fairly big flywheel press with a 11 kW motor then sufficient ramp up time is required. Using automated star delta starter with 30 sec. delay would not be enough.
Soft starter is the most economical and effective solution for 11 kW motor compared to star delta starter which costs a bit more (max starting time 10 sec.)
Another thing is in some cases bigger soft starter is needed if the load is too heavy at the start up (then it might not be cost-effective anymore).
Does striving to preserve the manual star delta starter would be the best thing to do?
Manual change over must be carried out depending on the assumptions of machine operator.
Unpredictable transition times between star/delta change over can cause massive current and mechanical spikes.
Thanks a lot.
 
Last edited:
It is, we have a 400kW rocking up shortly for a panel build.

A soft starter would be a cheaper option.
 
It is, we have a 400kW rocking up shortly for a panel build.

A soft starter would be a cheaper option.

Even that's not massive.

Had to go out to China last year to look at some SCADA work, the site had a 56MW drive.

Price between a decent SS and a VSD for an 11KW motor wont be a great deal different.

It's if he will have to upgrade the safety requirements of the press that's going to be costly. An by modifying the circuit away from a SD starter unless it meets all current legislation he will have to.
 
Then why worry about it, change the contactor that has burnt out. Job done.

Since I can't find the wiring diagram for manual star delta starter I had to reverse engineered it to some point (manual changeover lever auxiliary contacts in series with contactor NO latching contacts).

The contactor is old type with integrated overload protection, the construction is quite unusual so it's hard to figure out the exact wiring.

Another culprit is the casing without din rail. To fit a standard contactor new set of pushbuttons must be fitted and holes drilled.
 
Last edited:
Since I can't find the wiring diagram for manual star delta starter I had to reverse engineered it to some point (manual changeover lever auxiliary contacts in series with contactor NO latching contacts).

The contactor is old type with integrated overload protection, the construction is quite unusual so it's hard to figure out the exact wiring.

Another culprit is the casing without din rail. To fit a standard contactor new set of pushbuttons must be fitted and holes drilled.

But you'd have to do all that if you were installing a VSD or a SS. Plus it sounds like the safety system will not be up to standard, this will dwarf the cost of the VSD/SS
 
Thanks for answers. Attached some DIN rail on existing enclosure and used new star delta starter since the star delta starter kit with a 9 Amp overload protection relay was already purchased in a hurry.
According to starter enclosure nameplate it was only a 7.5 kW (10 hp) 15.9 FLA motor (due to plaque couldn't see anything on a motor nameplate), 7.5 kW soft-starter would have been more expensive on average.

Will have to ask for permit to upgrade the safety measures up to current requirements.
 
Last edited:
i have put a soft start schneider/ telemec altistart 22 on a 110kw 3ph motor thats drives a Flywheel forging hammer thats works lovely, I have 30secs for start time but i can set to 2mins if i wanted too, they are so much better no arcing contacts !
 
Last edited:
i have put a soft start schneider/ telemec altistart 22 on a 110kw 3ph motor thats drives a Flywheel forging hammer thats works lovely, I have 30secs for start time but i can set to 2mins if i wanted too, they are so much better no arcing contacts !

Are they slightly over-sized?
I think 10 secs is enough to reduce initial mechanical stresses.
 

Reply to Motor starter recommendations for flywheel press in the Commercial Electrical Advice area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
267
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
762
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
754

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top