L

leestaf

Hi Guys
I have had little contact with industrial motors and switchgear but would like to broaden my knowledge and would like some help.When choosing a motor starter what must be considered? obviously the loading and the voltage (230v or 400v), with or without isolator also overload protection of motor circuit and how to work this out. I was asked if i could recommend a motor starter for a small single phase motor on a small conveyor but with little experience in this field i couldnt.
College went into basic motors and the various types but nothing specific, does any one know of any courses on this?
Im not totally green just thought id ask my peers! 80)
 
The regulations state that an overload protective device must be fitted for any drive of 0.37kW and above. The important thing to remember is that the device should be set at the rated flc of the motor.
 
The important thing to remember is that the device should be set at the rated flc of the motor.

As a general rule of thumb. But some motors have different duty cycles as do overloads. I’m afraid that “regulations" are sadly lacking in the field.

Modern thermal overloads you would set to 100%, where as dashpots to 115%.

Foundry crane motors using dashpot O/L’s would be set at 150%. OK they are a breed apart. Built like tanks and nearly indestructible, I think I’ve changed about 5 in 35 years. Only one was a winding failure.
 
i was taught to set thermal magnetic overloads to 110% of the FLA, and ive been taught to set VSD's to 105%. i beleive its to stop nusiance tripping during voltage fluctuations, which may cause increased current to be pulled, but im not 100%. can anybody enlighten me please?
 
John, you have to look at the motor and O/L’s as a combination.

The sauce for the goose isn’t always right for the gander!

I’ve had to upgrade a MCCB from 4000A inrush to 7000A just because we had a policy of all replacement motors had to be “high efficiency”. The original motor started fine, the new one……
 
Another question :

if Inverters are put in circuit and the old Allen West over loads are left in would this cause nuisance tripping ?
 
I would recommend setting up the inverter as the overload protection and removing any older type thermal overloads.
 

Reply to Motor Starters and overload protection in the Electrician Talk | All Countries area at ElectriciansForums.net

Similar Threads

  • Question
Understanding the Problem: It sounds like your fridge's compressor is creating electrical interference when it kicks in, causing drops in your...
Replies
8
Views
934
Posted this to the DIY section since I'm not a business or employee in this matter but it feels more appropriate (and might actually get...
Replies
0
Views
1K
This is important. If the overload was originally connected in the supply lines it needed to be set to the 38A FLC, not the 0.58x FLC (22A) which...
Replies
19
Views
6K
  • Question
Nice one,thanks!
    • Like
2
Replies
34
Views
4K
  • Question
Ok Dave thanks, no more accidents yet 🙏😂….
    • Like
    • Informative
    • Winner
Replies
6
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks