Hi and thanks for any replies.
I am predominantly an install electrician and don't have a lot of experience dealing with motors so any help would be greatly appreciated.
I have been asked to connect a CNC machine, a dust extractor and a pump.
The CNC is straight forward as it is just connected to a rotary isolator, however the pump and extractor are just free standing motors and the name plates are in Chinese. I know the pump is 5.5 KW 3 phase and the extractor is 3KW 3 phase.
1. Am I right in thinking both should be wired through DOL starters with I think when calculated results in a 8.5A and 4.8A overloads with 0.9 power factor correction. (Guy who sold machines said rotary isolators were adequate for starting the motors)
2. Up to what size motors can a DOL starter be used.
3. How do I determine if they should be connected in Star or Delta as can't tell from name plate (What would happen if I connected them up wrong, ie connect in Delta and should be Star or vice versa?)
4. Am I right in thinking a DOL starter should always be used with motors because it provides protection to windings on start up and also it prevents motor restarting on power failure.
5. How do you determine if a Star Delta starter should be used with a motor?
Thanks again if you have got time to explain.
I
 
Motors of this size will need proper start circuits with overload protection. I don't think a rotary isolator will cut the mustard. I bet if it needs a pump and extractor that big the machine drive motor will need proper protection as well.

Did it not come with a starter or control panel or would there be any chance you could track down it's original owner to find out if it's available?

Also I would go back to "the guy" and give him a slap. If he doesn't know anything about motor control then tell him to S.T.F.U. with his dodgy info.
 
Geez that is an open ended question, there are multiple ways of starting a SCI motor DOL, SD, VFD and others with each being suitable for the demands on the motor and the type of drive required.
 
The CNC is a complete unit with connection terminals for the supply. It was just the extract and pump motors that don't have starters etc. They are independant machines to the CNC so I just thought I could connect them up through a rotary isolator and a dol starter.
They are new machines and when I asked the seller how to wire up he just said he doesn't have anything to do with the electrics and he said I was the electrician not him.....
 
Just remembered I took pictures of the plates. Am I right in thinking they are connected in star? 380v? Thanks again

[ElectriciansForums.net] Motors and Star Delta Question


[ElectriciansForums.net] Motors and Star Delta Question
 
hmmmm, no CE mark to be found on both those motors...

Not fit for purpose according to the low voltage directive.
Hi Lee, not doubting your statement regarding the "low voltage directive" in any way, but any chance toucould link the chapter/passage you are referring to, just interested that's all.
 
380V doesn’t really sound like a motor intended for the UK market, or at least not one started by simple DOL or similar. You’ll need something that can give the motor the voltage it needs.

As to whether you start it DOL or by other methods it can depend on the incoming supply.
If the incoming supply is big enough to cope with it then you can theoretically start any size motor DOL, but whether you should or not, or whether it’ll break the machine is another question.
 
This is a lot more complex than I thought.
The machines are all fed from a 3 phase transwave 22kw converter. (no 3 phase supply to building)
So am I right in thinking the motors can be supplied via a dol starter with overloads set at flc and connected in star or am I totally wrong and shouldn't get involved. Unfortunately like I said my background is more install work.
From nameplate if there is no drawing how do you determine if motor should be connected in star or delta?
Thanks to all for comments and if anybody can explain in layman's terms it would be appreciated.
 
the 3kw plate seems to show star connections

i was under the impression that rotating machinery needs contactors for start up and emergency stop local to machine for when the farmer gets his tie stuck in the rotary parts
 
the 3kw plate seems to show star connections

i was under the impression that rotating machinery needs contactors for start up and emergency stop local to machine for when the farmer gets his tie stuck in the rotary parts

Not always. Some machines use ‘safe torque off’. No contractors necessary.
 
Dol starters have stop starts on them so doesn't that satisfy emergency switching?.
Aren't dol starters just contactors with overloads built in?
I also read up on CE marking. I will let customer know!
I am meeting supplier of machines Wednesday so that should be interesting.
Thanks again
 

Reply to Motors and Star Delta Question in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
715
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
3K

Similar threads

  • Question
I believe that it is incorporated into the 5 days. But will double check. Thanks.
Replies
6
Views
1K
Hi, Thanks for that, you learn something new almost every day! Regards Griffey
Replies
5
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top