Thanks for that, moose. If type c is fitted with an rcd pod to convert it to an RCBO, am I correct in saying that Table 41.3(b) isn't relevant re max Zs value of that circuit, so long as the RCD test proves satisfactory?
 
Point 1, an MCCB is not a MCB, and don't come in Type designated tripping curves..

Point 2, Any RCD protection on a TN system is classed as ''Additional'' protection, so therefore your primary ADS system should be in place and functionally conforming to the circuits requirement!!

RCD protective devices are not, cover-all get out of jail cards, to be used to cover up an inadequate ADS on new circuits...
 
That's the first time I've heard this. So Zs needs to comply with the disconnection times regardless of any RCD. Is there not the possibility that the rcd can be added because the Zs is too high for ADS?
 
Well why would you install a circuit, that didn't conform to the protective devices Zs requirements in the first place??

I'm sure that many here think it's perfectly legitimate, the problems come when the RCD fails to operate. You are literary putting all your trust on a not so reliable RCD component/element rather than as an addition to a solidly connected earthing system....
 

Reply to Moulded Case Circuit Breakers in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
372
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
938
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Given the apparent lack of earth, combined with no short circuit or over current protection, I'd contend that luck has been the sole factor...
Replies
5
Views
601
nicebutdim
N
I used to dislike Chint domestic circuit breakers, always thought they felt a bit cheap and nasty but that said I never heard of any particular...
Replies
9
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top