My friend is building a house and his 3 phase metre is about 60m across a field.
I was wondering could i just take out the metres and put in a 3 phase 80amp isolator and run a 25mm 4 core SWA cable from there to the new location?
Could any one suggest anything easier, or cheaper?
 
Any of the energy suppliers can trace the MPAN if you quote them the whole meter ID number and the post code.

Also, do you actually need a 3ph system on a house build? It would be cheaper to get a whole new supply put in and probably a much cheaper 1ph would suffice.

Oh, and you probably won't satisfy your voltage drop requirements with that size of cable over that length, btw.


Will have a look for code on it.

Yes he needs 3 phase for machinery in garage.
 
I know it's money NOT going in your pocket, but you'll find the DNO's will charge less for a whole entire incomer move than you could even buy the cable for to extend it, plus have no worries about Vd and also probably get a better Ze out of the deal, too.
 

Reply to Moving 3 phase supply in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
771
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
978

Similar threads

Just stick the 63amp fused connector before the Henley block , or Lucy block as you call it, and your all good, as for your 2nd point, , the...
Replies
1
Views
1K
Good question now to start with thermosetting insulated conductors are not tri-rated that is something different. Table 4E1A deals with this type...
Replies
1
Views
280

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top