Moving the CU | Page 2 | on ElectriciansForums
Discuss Moving the CU in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
no-one is saying dont test or dont check over installation prior to any work , it was a question of which cert.
instead we get the usual drama queen crap on what if someone dies ?
i'm sure loads get killed every year from excessive R1+R2 readings.
I personally would issue a completion certificate due to the fact I had interfered with all circuits and would want to ensure they were safe and sound after re-connecting, plus it is my name of the certificate saying it is safe for a family to live in the house after the works.
I wouldn't be testing in case someone dies, just to make sure everything was as it should be. The other reason for testing the full range would be to cover myself if other subsequent work generated a fault. I would have a dated record of the readings at the end of the work I'd completed.
and all your customers are happy to pay for this extra service ?
What extra service? I'd only test the circuits I'd worked on, which is all of them, and issue the appropriate paperwork, which would be an EIC.
Move the cu extend circuits issue MW for each circuit.....................simples.............why the protracted debate?
Because were british and never agree about anything, our Island is 900 miles long and yet we cannot even speak with the same accents lol, never has there been a country like ours in history, we love debate and love trying to beat each other, thats just brits for you. :santa3:
Morning
don't think the OP (Hi Amp) was going to extend any circuits, is that right? Just move the CU. I assume from your post the situation did not require extension of any cable?
A customer wants a consumer unit moved about a meter to one side, because she's converting the garage and wants to put a door where the consumer unit is now.
Moving it a metre must involve extending the cables surely? Especially if a door is going where it was originally.
Installation cert for me.
Removing old CU modifying every circuit then re-installing CU.
Last person to work on it.. you
Extent of installation affected by your work.. all of it.
I would just knock the wall down and hang the cu on the back of the new door, no drama, 2 screws, easy.
Good call,but surely hanging the CU on the door will require all circuits to have new flexible cables which,will require testing.Its a mine field....
What is a completion certificate?
Ok, so you are moving a CU, you need to extend the circuits, appropriate box, wago's etc, extend out no worries.
You are not doing an EICR. You are doing a CU change. You do the standard CU change tests, Ze Zs's Insulation tests, all that you need to do to fill out an EIC. In the EIC is a section that details the extent of the work carried out. You put 'Replacement of consumer unit and associated testing only' so long as you can fill out the cert honestly, you are covered.
Should you uncover any problems during the testing you need to to do to complete ther EIC then yes, you need to investigate, eg you cant just shove an R1 of 0.70 in there followed by a 2.5 R2, you will need to investigate that, but that is as far as it goes, if it all adds up and your insulation tests are fine, you are covered.....
but its not a cu change, it is relocating the same cu. Unless i read the post wrong which isnt unknown.
So how many when they extend a ringfinal issue an EIC? not me.
So if its the same cu just relocated (no change in ocpd's or rcd's) & the circuits require extending why would you complete an EIC?
Reply to Moving the CU in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
I would hazard a guess your electrician may be able to contact your DNO and have the switch swapped to a MFS very quickly..
But why do they want a CU? That won't give them any more available power than they currently have. As it is a 2.5mm SWA cable it is presumably a...
davesparks