I have a Metrel MI3000 MFT. It has given very low insulation resistance readings for a circuit I was testing earlier today (0.001MΩ) between live and earth(!) but the circuit has been working fine and not tripping the MCB (20A, no RCD as it is a pre-17th ed. CU) and I had tested it only a couple of weeks before with the same MFT and got 81MΩ between live and earth. There has been no work done on the property since that test that could have damaged the circuit (owner says he hasn't so much as put up a picture hook). The battery in my MFT was getting quite low and I have previously noticed inconsistent results with a low battery. Has anyone else had any similar experiences or have any idea if I might be thinking along the right lines in thinking the low battery might be giving misleading results. I have arranged to go back and re-test tomorrow, with a charged battery!