Hi, first off apologies if this is a daft question I’m having an absolute mental block..

Scenario is:

I have three rooms all on the same circuit and all controlled via a one way switch, i need to put a PIR in each room, now would this not operate all the rooms regardless of which room someone walked into?

How do I resolve this so I end up with a PIR in each room that only operates the lights - which are off of kliks/Greg’s in the ceiling void - in that room!?

Any help massively appreciated
 
First off blank the switch to give every room a pl

Then drop the live Greg feed into pir
Out of pir into light

Plenty of lights now com with a microwave senser as a option in that case Greg flex straight into light
 
So will the PIR(s) switch on all lights still? Are we talking suspended ceilings? Presumably 20/25mm conduit as well? So you may have to put in a perm. live for the PIR as most I have used require L and N then sw. L from the PIR. I usually use 4c. flex to the PIR with the L and N plus the switch out to the light on a 4 pin Klix.
 
now would this not operate all the rooms regardless of which room someone walked into?

Yes if it is on one circuit and you are planning on wiring the PIR's up in parallel from the existing switch wiring it will illuminate all rooms.

To achieve this you will have to split existing circuit (or rewire) As each PIR will require a switch wire to lighting in the required rooms only.
 

Reply to Multi room PIR help needed in the Lighting Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
380
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
956
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

SOLVED Thanks for all the help. It was nothing to do with the smoke detector. In this new hole (where there will be a light fitting) three white...
    • Like
2
Replies
24
Views
3K
  • Question
I have to agree with Baldelectrician on almost everything he says except one ! I wouldn’t be walking away I’d be running lol. Definitely if your...
Replies
13
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top