Would the cpc not have sufficient surface area though with a16mm t/e with it only being 6mm
What does the adiabatic say?
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss Multiple consumer units in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
Would the cpc not have sufficient surface area though with a16mm t/e with it only being 6mm
Theoretically but it will be deeper than 50 mm
What size OCPD are you planning on using for the 4 x distribution circuits?
Do do you mean on each of the submain boards ?
The over current protective device that is protecting each 16mm T&E.
63amp each I was planning to use
63a 30ma rcd