I have a metal Hager sub CU, 10 way RCBO, installed in 2018 in an accessible attic space, this sub-CU being fed from another unit close to the meter. The two are connected with 10mm 3 core SWA: line, neutral and CPC. At the end close to the meter, the armoured cable metal sheathing is earthed as usual, by being attached with a brass interior use gland to the metal box CU plus a wire going from the gland bolt to the earth bar. The earth wire in the SWA is properly connected at both ends.
At the sub-CU in the loft, the brass gland is bolted to thick plastic trunking and the internal wires go through this, via holes top and bottom, to the CU. However, the brass gland itself only makes contact with the top section of plastic trunking, there is NO connection between the protective wire sheath and either the metal CU or the earth bar inside it.
I would expect the wire sheathing to be attached to earth at both ends? Obviously it is easy to remedy but I would like the opinion please of qualified domestic installation electricians as to whether it is correct NOT to earth both ends of the sheathing or whether this is most likely an oversight or error by the installing electrician. I am not seeking to blame him for anything - I just want to understand.
At the sub-CU in the loft, the brass gland is bolted to thick plastic trunking and the internal wires go through this, via holes top and bottom, to the CU. However, the brass gland itself only makes contact with the top section of plastic trunking, there is NO connection between the protective wire sheath and either the metal CU or the earth bar inside it.
I would expect the wire sheathing to be attached to earth at both ends? Obviously it is easy to remedy but I would like the opinion please of qualified domestic installation electricians as to whether it is correct NOT to earth both ends of the sheathing or whether this is most likely an oversight or error by the installing electrician. I am not seeking to blame him for anything - I just want to understand.