I have been reading a little about bonding and outbuilding supplies and have just had a thought.

My father has a metal framed greenhouse with a socket inside supplying a heater.

The heater is metal and the socket is metal clad.
The supply is TN-S and I am not sure of the loop impedance, I can measure it tomorrow.
From what I have read I am now of the opinion that this metal frame should be bonded back to the MET in the house.

I can use the adiabatic to work out the size of bonding conductor.

The greenhouse is made primarily of glass but with a steel frame.

The other thing is the supply is an underground lead sheathed TN-S cable that runs about half a mile to a transformer on a pole in the field out back.
There is so much of the metal sheath connected to true earth on the long run back that it kind of acts like an enormous earth plate if you know what I mean.
The lead sheath is then connected to the transformer which itself has a long earth cable going into the ground.

Do you think this greenhouse needs bonding?

Thanks.

P.S. one more thing, the ground is clay and very damp and soft, if a TT were installed I would imagine a very low reading could be obtained.
 
Last edited:
Here's the transformer:

[ElectriciansForums.net] My dad's greenhouse[ElectriciansForums.net] My dad's greenhouse
 
OK I’m being facetious here. TT it with a spike at each corner, it’ll keep it tied down when it’s blustery.

I’ll never forget how upset my father in law was when the wind took his beloved green house. “Stuff the greenhouse, what about my chrysanthemums!” The only year in all the time I’ve known him he didn’t win a prize for them.
 

Reply to My dad's greenhouse in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
293
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
802
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
834

Similar threads

  • Question
Why would the RCD fail … yes it can happen but then it may not. Without it you have no protection on the TT System
Replies
36
Views
4K
I am living in the north of Thailand outside of the big city. That means in the rainy season we have multiple times per week power outages...
Replies
0
Views
456

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top