My first EICR and I'm confused! I'm industrial this is domestic
Hi,
I'm an industrial spark and taking my 2391 next week (wish me luck, I need it).
I decided to get a bit of practice and started an inspection on my own house.
I got as far as, b32 socket (ring?!) breaker looks slightly browned, better check it.
3 cables in the breaker two identical and one that appears to be a spur to an adjacent socket.
Q1) Let's start with the adjacent socket as that one should be easy:
It's a double socket.
There is no way a load can be put on that will stress the 2.5mm without blowing the bs1361s...however, the 2.5 is undersized to the b32.
clearly dodgy, but just curious how some experienced guys would treat this.
Q2) Ok now for the confusing bit.
The 'ring' is only a ring on the N. Live and E are open.
All sockets pass inspection (well small arcing on one N, which is fixed)
IR passes (on this circuit).
The board is split RCD so a borrowed N would take out the RCD.
All sockets have an in/out feed apart from one.
r1/r2 unsurprisingly no reading.
r1/rn would have been a bit more interesting, but haven't done yet.
Does anyone have any advice, this seems a strange one?
The fact you have open end to ends on the lines and cpcs is an issue which would attract in most people's eyes a Code 2. The fact you have continuity across the neutral conductors suggests it was a ring final circuit.
Hi,
Why is it dodgy to not have overload protection on a cable (spur) which cannot be overloaded?
433.3.1 would clearly be applicable
If you have a break in the rfc then it would automatically require a C2.
It needs fixing, either split into two at the break in which case both would need 20A mcb, or fix the fault.
wow, thanks for the fast responses!
I've been doing my best to memorise GN3.
It's doing the ring tests that I've come across the faults.
That's why I'm asking, I'm checking what the skilled inspectors think.
If there was a short on the back of that socket the cable would potentially (not done the calc) overheat before the b32 trips. So there is a small chance of an unprotected fault.
433.3.1 nails it, thanks.
I would have thought C1, can you explain why C2?
My thinking is that the circuit can overheat in non-fault conditions hence C1. Functionally I've got a 2.5mm spur that can happily maintain 32A without a trip.
So the simple solution is a break in the L/E, it just seems such an unlikely fault to me. Is there anything else that I could be overlooking, or is it time to start ripping up floorboards before my house burns down?
Downstairs
spur
Zs - 0.25 - Zn - 0.19
Near socket
Zs - 0.54 - Zn - 0.31
Far socket
Zs - 0.58 - Zn - 0.35
Upstairs
Landing
Zs - 0.38 - Zn - 0.26
Vlad's bedroom - Spur
Zs - 0.43 - Zn - 0.31
Mordecai's bedroom
near 0.46 - 0.3
far 0.39 - 0.26
My room
0.33 0.29
I'll check for patterns shortly, but pizza has arrived.
Thanks for the help, understanding how other people tackle problems is good training.
We cannot assume the breaks have occurred in the same place but you will have to carry out contuity tests. Have you tried an insulation resistance test across the open ends to see if there is a tenuous connection.
Downstairs
spur
Near socket
Far socket
Upstairs
Landing
Mordecai's bedroom
near 0.46 - 0.3
far 0.39 - 0.26
My room
0.33 0.29
If there is a short then it would be a fault, normally this is assumed to be zero resistance and therefore your Zs check would show it would disconnect within .4s - if it is a high resistance arc, then yes it could pass just enough not to trip due to fault, but more than the cable rating (remembering the arc itself is more of a likely fire issue than being able to overheat the cable over several hours).
Why C1 - C1 means it is an immediate danger (for example live contacts exposed)
Why C2 - C2 means that there is a danger if something else occurs to cause the danger.
In this case it doesn't present an immediate danger, there has to be a previous problem (overload etc).
As to where is the fault, you can usually narrow it down without ripping up too much, split the rfc at the cu, short one end l-n then go round the sockets looking for l-n continuity (just use the standard plug from the mft - no need to remove sockets), then repeat for the other end, this generally narrows it down to between two sockets (then it's a bad connection in either socket, or the cable between).
Then repeat for the cpc
There is no guarantee that you have just the one point of fail - you may find a couple of breaks in the same conductor and/or different points of break between conductors.
Good to know, thanks.
urgh, just thought about this more.
OK I now get why it's not a C1 for the reason I gave (someone would need to plug something in to make it overload).
However, you mentioned arcing and fire...
Is that not an immediate problem?
Or is the arcing a cause that could create a future problem (fire) which is why C2?
You mentioned a short at the back of a socket, how could you get that unless it was either a full short , or an arc causing just the correct amount of current?
This fault could occur anywhere.
The likelihood of an arc occurring with just the right amount of current to not cause a fault protective device to trip, but cause a fire is the same irrespective of what you have found to date.
If there is a reason to believe a fault such as this would occur then yes that particular issue may draw a code.
The spur wouldn’t overload because as a double socket, the most that can be plugged in is 2 x 13A… 2.5 cable can take 26A, (although the double socket itself might struggle!)
If a dead short, then the 32 breaker would trip.
Looking for the fault could be the case of taking off every socket and testing every cable between. There may be hidden joints you yourself are unaware of, even if it is your own house.
And… unfortunate positioning of dodgy advert on previous message……
Inteificio,
pc1966,
TrueNAS JBOD Storage Server