Hi all,
After some options/opinions on fault finding N/E fault on ring final as fairly newish to being out alone.
Customer wants to upgrade from rewirable CU to RCBO so fairly old wiring but no signs of cable breakdown or anything totally messy on inspection. This circuit basically holds everything inc. boiler etc but exc. lights and cooker.
Ring continuity tests are slightly messy but well within limits.
IR testing L/N & L/E = approx 150M, however N/E = dead short @ 0M
Unplugged everything, isolated all FCUs that I can find but still no luck. Temporarily tried the circuit on a RCD to check I hadn’t missed any loads or just being an idiot but it only holds for a minute or two before it trips confirming a fault.
My thoughts are to now break down the legs of the ring and go hunting the fault similar to finding a continuity fault.
Any one have any other options or go to places to start that might speed up the process??
Cheers in advance.
After some options/opinions on fault finding N/E fault on ring final as fairly newish to being out alone.
Customer wants to upgrade from rewirable CU to RCBO so fairly old wiring but no signs of cable breakdown or anything totally messy on inspection. This circuit basically holds everything inc. boiler etc but exc. lights and cooker.
Ring continuity tests are slightly messy but well within limits.
IR testing L/N & L/E = approx 150M, however N/E = dead short @ 0M
Unplugged everything, isolated all FCUs that I can find but still no luck. Temporarily tried the circuit on a RCD to check I hadn’t missed any loads or just being an idiot but it only holds for a minute or two before it trips confirming a fault.
My thoughts are to now break down the legs of the ring and go hunting the fault similar to finding a continuity fault.
Any one have any other options or go to places to start that might speed up the process??
Cheers in advance.