Hi all

can anyone give me the logic why the RCD wouldn’t trip on a neutral/earth fault. Testing a extension where they have added in 5 additional sockets to the upstairs ring had been powered up and nothing tripping with household appliances plugged in and working. Carrying out IR tests to find had dead short on one leg of the neutral and earth between 2 sockets but there was no issue of tripping ? RCD checks out ok with test button and RCD tests. Have disconnected this leg and then fitted fuse spur off the ring to carry the additional sockets now as to late to add in additional cable, so extension spurred off ring using fuse spur. Would it be the case that it had seized a bit RCD or that its connected to a TNCS system?? Replies much appreciated ?
 
On both tests at 250v and 500v. I tested live to earth at 250volt seen that it was very low near enough zero, now this has been connected to a RCD and MCB for years this circuit. So I then joined live and neutrals together at consumer unit then tested live to earth IR test at nearest socket comes up >999mega ohms. So I am thinking I’m testing through the USB points when carrying out live to earth only with neutrals still connected to N bar ?? That make sense
 
On both tests at 250v and 500v. I tested live to earth at 250volt seen that it was very low near enough zero, now this has been connected to a RCD and MCB for years this circuit. So I then joined live and neutrals together at consumer unit then tested live to earth IR test at nearest socket comes up >999mega ohms. So I am thinking I’m testing through the USB points when carrying out live to earth only with neutrals still connected to N bar ?? That make sense
Testing at 250v is only beneficial when there is a fault so that you don’t need to subject circuit to 500v however you need to carry out insulation resistance test at 500v to record accurate fault reading and true scale of insulation. I’m trying to test you here ?
 
Testing at 250v is only beneficial when there is a fault so that you don’t need to subject circuit to 500v however you need to carry out insulation resistance test at 500v to record accurate fault reading and true scale of insulation. I’m trying to test you here ?
I’m here to learn just like yourself and Aslong as it’s done appropriately then there is no harm. Best way is to ensure everything is unplugged from sockets
 
If it’s dead short L-E should be a banger? Is it old consumer?
These are the jobs I hate, because you have to explain to customer that it’s not right even though it appears fine and well. Don’t leave it there find the fault and charge accordingly you’re the last sparky there so when you close that door it’s your neck on the block
 
No it’s 6 months old, that’s why I am thinking I’m testing through the USB ports only thing I can think of as if it was a dead short then it would show up on L- N together and test to earth as well but it’s clear ?
 
No it’s 6 months old, that’s why I am thinking I’m testing through the USB ports only thing I can think of as if it was a dead short then it would show up on L- N together and test to earth as well but it’s clear ?
Well disconnect the usb sockets put the cables in connector blocks then test. Make sure you are disconnecting the circuit in question out of bar/mcb to ensure it’s definitive. I’m a bit confused here sorry it’s late and been working 14 hours again ?‍♂️ You’ve been called back after 6 months and it’s tripping?
 
Well disconnect the usb sockets put the cables in connector blocks then test. Make sure you are disconnecting the circuit in question out of bar/mcb to ensure it’s definitive. I’m a bit confused here sorry it’s late and been working 14 hours again ?‍♂️ You’ve been called back after 6 months and it’s tripping?
The USB ports will 100% interfere with you’re readings and give false readings disconnect them. So the fault is on the sockets? Unplug everything and then carry out insulation resistance. Once established that the fault is on the ring main. Most likely pain in the arse is N-E fault split the legs at consumer go to half way point of ring (take an educated guess) then you will know which side the fault is on)
 
Sorry no the consumer unit is 6months old, this was a extension that got done and they require test cert. yeah think best to disconnect but then test kind of pain in the arse tbh is it disconnecting circuits ?
 

Reply to N/E fault RCD not tripping ?? in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
446
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Seen this where T&E has been fixed with a flat bend of too tight a radius.
2 3
Replies
35
Views
2K
Yup will do exactly that when I'm back down there. Thanks for the help
Replies
6
Views
392

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top