Hello Sparkies, …..I need advice.
I currently have a ceramic hob that is on a dedicated 30 amp circuit and a fan oven with a 13 amp plug on the ring main.
The oven has reached the end of its life and I have to buy a new one, at the same time I would like to change the ancient hob for a new induction hob.
I would like to know if the same 30 amp circuit can be used (using a splitter) to hard wire both the hob and oven and meet current regulations.
My understanding (from what I have read on the web) is that maximum load for a 30 amp circuit would be 240 volts * 30 amps = 7200 KW. Allowing for a 20 % safety margin that would give me 5.76 KW for an oven and hob combined.
I have found an affordable oven (2.4KW) and induction hob (2.9KW) combination that I like totalling to 5.3 KW.
Are my calculations correct? Would it be safe and legal? Could I get a combo closer to the 7.2 KW? Or do I need a higher rated circuit?
Thanks and best wishes,
antonio
I currently have a ceramic hob that is on a dedicated 30 amp circuit and a fan oven with a 13 amp plug on the ring main.
The oven has reached the end of its life and I have to buy a new one, at the same time I would like to change the ancient hob for a new induction hob.
I would like to know if the same 30 amp circuit can be used (using a splitter) to hard wire both the hob and oven and meet current regulations.
My understanding (from what I have read on the web) is that maximum load for a 30 amp circuit would be 240 volts * 30 amps = 7200 KW. Allowing for a 20 % safety margin that would give me 5.76 KW for an oven and hob combined.
I have found an affordable oven (2.4KW) and induction hob (2.9KW) combination that I like totalling to 5.3 KW.
Are my calculations correct? Would it be safe and legal? Could I get a combo closer to the 7.2 KW? Or do I need a higher rated circuit?