Afternoon all. Working on a kitchen extension and the customer has just taken delivery of a rangemaster induction hob and oven combined. Ind is 11.1 kw, total seems to be 16.2 kw. I am calculating this as 27.5 amps. Can anyone else confirm this or am I missing something? Need to ensure I fit the right cable size. Thanks Michael
 
Without the full specs it's hard to say, however I'd say put it on a 10mm/40A cct if you can just for future proofing but don't lose any sleep over 6mm/32A.
 